Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82501members
350088posts

1u 750 UPS - Replaced Batterys but not clearing error

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
leonr_apc
Crewman
Crewman
0 Likes
5
156

1u 750 UPS - Replaced Batterys but not clearing error

This was originally posted on APC forums on 9/29/2011


Hi,

Basically, all charge lights were flashing (its been this way for a while), then recently the red battery light illuminated (no beeps).
I ordered new genuine APC batteries and replaced them as normal, however the lights are still flashing and the battery failure/replace light is still illuminated.

Any ideas? (Batteries have been in for nearly 24 hours).

Cheers,
Leon


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
155

Re: 1u 750 UPS - Replaced Batterys but not clearing error

This reply was originally posted by Dakota on APC forums on 10/1/2011


No it wont, If the battery is bad it will switch back to on line operation

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
155

Re: 1u 750 UPS - Replaced Batterys but not clearing error

This reply was originally posted by Chris on APC forums on 9/29/2011


So currently which leds are lit up? Did replacing the battery clear the replace battery LED?

leonr_apc
Crewman
Crewman
0 Likes
0
155

Re: 1u 750 UPS - Replaced Batterys but not clearing error

This was originally posted on APC forums on 9/29/2011


Unfortuantly not, thats my main concern.

Currently we have the 'x' in red (battery failure/replacement light) and the % charged lights are all green (all full lit) and flashing together. The red light is solid.

So that to me means batteries are not working and you get less than 2 minutes if the power fails. However I don't understand why the battery light has not gone off after replacing the batteries... do I need to do a self test? I don't like messing with them as we have live servers connected.

Cheers,
Leon

BillP
Administrator Administrator
Administrator
0 Likes
0
155

Re: 1u 750 UPS - Replaced Batterys but not clearing error

This reply was originally posted by Dakota on APC forums on 9/30/2011


You need to preform a self test then run time calibration

leonr_apc
Crewman
Crewman
0 Likes
0
156

Re: 1u 750 UPS - Replaced Batterys but not clearing error

This was originally posted on APC forums on 9/30/2011


Thanks!

Will performing a self test cause problems to the power output? (live servers etc)

I don't think it will, but I would like to check.

Cheers,
Leon

BillP
Administrator Administrator
Administrator
0 Likes
0
156

Re: 1u 750 UPS - Replaced Batterys but not clearing error

This reply was originally posted by Dakota on APC forums on 10/1/2011


No it wont, If the battery is bad it will switch back to on line operation