1500RM with AP9631 Management Card will not start after power is restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
amroberts_at_interact.ccsd.net_apc
Crewman
Crewman
0 Likes
2
262

1500RM with AP9631 Management Card will not start after power is restored

This was originally posted on APC forums on 11/5/2012


I've been testing configurations on my 1500RM units. We've pulled power on the unit and let it drain the battery to the point the unit shuts down. When we apply power back to the unit, it does not start back up. We have to manually start it or start via the management card. Attached is the config.ini file. Please let me know if there's any other info I can provide.

Thank you!

Tags (3)

Accepted Solutions
amroberts_at_interact.ccsd.net_apc
Crewman
Crewman
0 Likes
0
262

Re: 1500RM with AP9631 Management Card will not start after power is restored

This was originally posted on APC forums on 11/6/2012


That was the issue. It just appeared that I didn't wait long enough. Thank you!

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
262

Re: 1500RM with AP9631 Management Card will not start after power is restored

This reply was originally posted by Angela on APC forums on 11/6/2012


i think i see the problem.

under the Smart UPS/Matrix section, you have:

ReturnBatteryCapacity=45
ReturnDelay=60

return battery capacity=45 means the UPS is going to charge up to 45% before it turns back on and then it will apply the return delay of 60 seconds as well.

so, I assume you did not wait for the UPS to charge back up to 45% + 60 seconds to see if it turned back on? this setting (return batt capacity) is good to set if you want it so that the UPS has some capacity/runtime before it turns everything back on and then potentially AC power is lost again.

amroberts_at_interact.ccsd.net_apc
Crewman
Crewman
0 Likes
0
263

Re: 1500RM with AP9631 Management Card will not start after power is restored

This was originally posted on APC forums on 11/6/2012


That was the issue. It just appeared that I didn't wait long enough. Thank you!