HI all.
I have installed "non smart" batteries into this UPS.

THe bank is made of 32x 105AmpH batteries. +, CT, - connect to UPS.
All working very well. However I am not sure what to put into the External Battery Cabit capacity setting.
Common sense would tell me to put in 105amh. However, although the bank is 384 nominal Voltage DC, the UPS seems to report Center Tap voltage. Ie 221 fully charged (442V) or 192 fully discharged (384V). This makes me think that it threats the top and botom as 2 banks,. ie. My amp hour should be 105 + 105 = 210.
However, after reading a extract on this forum, i am VERY confused. If i had to follow this, my amph would be 32x 105 = 3360ampH which is most definatelly not correct.
Quote: (https://www.apc.com/us/en/faqs/FA156609/)
"
In order to setup the external battery packs, please key in as (Ah of battery) x (total number of batteries).
Example 1: If there are 16pcs of 5Ah battery in series (for 5kVA), the total Ah number is 5Ahx16pcs=80Ah.
Example 2: If there are 16 pcs of 100 AH batteries in series(for 5 KVA), the total AH number is 100 AH x 16 pcs=1600 AH
Example 3: If there are 2 strings of 16pcs of 5Ah battery in series (for 5kVA), the total Ah number is 5Ahx16pcsx2 strings=160Ah.
The 80Ah inside the table is the default setting for 5kVA/6kVA (1 EXB: 16pcs of 5Ah battery)
The default setting for 8kVA is 140Ah (1 EXB: 20pcs of 7Ah battery)
The default setting for 10kVA is 180Ah (1 EXB: 20pcs of 9Ah battery).
If “Ext total battery Ah” is set as 0, it means there is no external battery connected. "