This question was originally posted by Ashfaq on APC forums on 8/23/2011
Dear,
We have a one UPS Model number SY32K96H with one extra power module SYPM10K16H, new installation giving critical alarm, When start UPS.Found these alarm
MDS: Communication Lost With Metering Board[7..12]
MDS: Communication Lost With Metering Board[1..6]
As we know there is no metering and no power distribution units in this model.
Please find attached logs file and give us advice what we will do to solve this problem.
Regards,
Ashfaq Ahmed
Posted: 2021-08-24 06:59 AM
Hi,
I noticed a few other things related to the menu apart from the missing switchgear option. Do you know what firmware is running on the system (both on the UPS Intelligence Module and on the Network Card)? Have you configured the network card and are you able to access it remotely?
Posted: 2021-07-29 09:44 PM
This reply was originally posted by Ashfaq on APC forums on 9/3/2011
Dear All,
I am waiting reply, but until now no body answer. I think no body known about this problem.
Regards,
Ahmed
Posted: 2021-07-29 09:44 PM
This was originally posted on APC forums on 9/6/2011
Hi Ashfaq,
>
MDS: Communication Lost With Metering Board \[7..12\]
MDS: Communication Lost With Metering Board \[1..6\]
>
Those alarms indicate that the UPS thinks it's configured to use APC's power distribution but cannot communicate with it. This will not affect the operation of the UPS.
>
As we know there is no metering and no power distribution units in this model.
>
Okay, if it doesn't come with APC's power distribution, then it's probably just configured incorrectly. You should contact APC phone tech support to make sure it's set up right. For this particular issue, you can change the power distribution configuration on the PowerView display under Switchgear->Factory to either "Other" or "None" so that it doesn't look for APC power distribution.
Posted: 2021-08-21 11:32 AM
Hi There.
I have the same exact problem.
Running a single row of batteries.
My problem is there is no switchgear option on the menu. It's missing alot of options if I compare it to the manual. This was a unit bought pre used. Was switched off 2 years ago and not touched since from what I been told.
You assistance would be greatly appreciated
In my case it's looking for 3x switch gears it can't find as they don't exist.
Posted: 2021-08-21 11:34 AM
Correcting mistake.
6 x power boxes on top.
3x power modules.
1 row of batteries with 4 units.
Apologies don't know how to edit post.
Posted: 2021-08-24 06:59 AM
Hi,
I noticed a few other things related to the menu apart from the missing switchgear option. Do you know what firmware is running on the system (both on the UPS Intelligence Module and on the Network Card)? Have you configured the network card and are you able to access it remotely?
Posted: 2022-07-04 05:12 AM
Maybe too late but I got the solution to this problem which seems to be the same as the OP.
My UPS stood completely dead for over 2 years.
What it took to make it work again was a firmware flash. Once I did that, it remembered what it was and all correct options were available.