Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82179members
349776posts

SMT1000RM2UC access

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

captainkirk
Crewman
Crewman
0 Likes
1
102

SMT1000RM2UC access

we had a SMT1000RM2UC on a shelf, and decided to put it to use.  we have it connected to the network, it has an IP address, but we cannot access it via web browser.

we did make a change on the UPS display, turning on "smart connect enable with control"

and 30 minutes later still no browser access, so not sure how to setup alerts and such on it?

Tags (1)
1 Reply 1
TonKei
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
58

Re: SMT1000RM2UC access

Hello

 

The smartconnect port will not provide you with a web UI for the UPS. It is designed to communicate with the smartconnect portal.

If you want to have a web interface toward the UPS itself, that goes beyond the functionality of the smartconnect portal, you will need a network management card, that is then installed in the smart slot port on the back of your unit.

 

Best regards

Tonny 