Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82169members
349765posts

Input Current for SRT10KRMXLI

APC UPS Data Center Backup Solutions Forum

Schneider Electric support forum for Data Center UPS, software and services including our APC offers designed to share knowledge, installation, configuration, and general product use.

Solved
kchoo_apc
Crewman
Crewman
0 Likes
5
411

Input Current for SRT10KRMXLI

This was originally posted on APC forums on 6/3/2016


Hi,

Can someone advice me what is the input current required for SRT10KRMXLI UPS? We have 3 phase 20amps, does it sufficient for this model of UPS? Thank you.


Accepted Solutions
kchoo_apc
Crewman
Crewman
0 Likes
0
411

Re: Input Current for SRT10KRMXLI

This was originally posted on APC forums on 6/5/2016


Bill,

     Thanks for sharing the installation guide.In deep wee have refereed to this spec but we are not sure which column of information to read.   We currently runs on 3 phase 20 A single feed, we would like to get your technical expertise to assist us to confirm that our current socket (3 phase 20 A) is sufficient to support SRT10KRMXLI UPS we plan to purchase. According to the spec, it stated “Current Full Load (nominal)” is 18 A and “External Input Circuit Breaker Mains (typical)” is 80 A, we are not sure what is the different of those 2 reading indicating about. Our electrician wants us to confirm that the input current required is the reading out from “Current Full Load (nominal)” is 18 A and not  “External Input Circuit Breaker Mains (typical)” is 80 A. Thank you for your advice.

 

 Question

See Answer In Context

Attachments
5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
411

Re: Input Current for SRT10KRMXLI

This reply was originally posted by Bill on APC forums on 6/3/2016


Kelly,

The installation guide list the required input and wiring.

http://www.apcmedia.com/salestools/SCON-9DETDD/SCON-9DETDD_R3_EN.pdf?sdirect=true

kchoo_apc
Crewman
Crewman
0 Likes
0
412

Re: Input Current for SRT10KRMXLI

This was originally posted on APC forums on 6/5/2016


Bill,

     Thanks for sharing the installation guide.In deep wee have refereed to this spec but we are not sure which column of information to read.   We currently runs on 3 phase 20 A single feed, we would like to get your technical expertise to assist us to confirm that our current socket (3 phase 20 A) is sufficient to support SRT10KRMXLI UPS we plan to purchase. According to the spec, it stated “Current Full Load (nominal)” is 18 A and “External Input Circuit Breaker Mains (typical)” is 80 A, we are not sure what is the different of those 2 reading indicating about. Our electrician wants us to confirm that the input current required is the reading out from “Current Full Load (nominal)” is 18 A and not  “External Input Circuit Breaker Mains (typical)” is 80 A. Thank you for your advice.

 

 Question

Attachments
BillP
Administrator Administrator
Administrator
0 Likes
0
411

Re: Input Current for SRT10KRMXLI

This reply was originally posted by Gareth on APC forums on 6/6/2016


If your electrician needs to ask that then it is time to employ a new electrician.

prince213_apc
Lieutenant
Lieutenant
0 Likes
1
411

Re: Input Current for SRT10KRMXLI

This was originally posted on APC forums on 6/6/2016


You need to fit 80A MCB's or 80A 4 pole MCB at distribution board. The 18A showing there is the typical load current which can range from 18A to around 54A. 8OA is the peak current which should not be exceeded in any case.

TellItLikeItIs_apc
Ensign
Ensign
0 Likes
0
110

Re: Input Current for SRT10KRMXLI

It’s a shame that some forum users don’t want to help others to learn.

 

This UPS can be supplied by either a single or 3 phase electrical supply. If supplied by a 3 phase supply, the load on each phase will be a maximum as was suggested (in the order of 20 Amps per phase). The supply becomes an issue if the UPS develops an internal fault and needs to switch to static bypass. When the UPS is in static bypass all of the input load switches to one phase (usually L1 depending how the UPS has been wired ). The supply would then be overloaded and trip.

 

your electrician may be very good but it sounds like he is not familiar with UPS’s or at least this model. I would suggest you use someone who is competent (has the necessary knowledge skills and experience of how to install and commission) this UPS. The individual should be able to demonstrate they have been trained by Schneider on this product and have experience of installing the same - this should not be their first time. They should also be able to commission the UPS correctly including updating the UPS firmware and configuring the network management card for you. 