Thank you Al! your knowledge of these products is excellent!!!
I read FA156154 though and it explains an error in how the Gen 1 NMCs (AP9617, AP9618, AP9619) report calibration events.
The FA notes that it does not apply to AP9630, which is the NMC we have, Hardware Revision 05 running sy3p v7.0.4 on aos v7.0.4.
I'm very tempted to retry calibration again to duplicate the error. But I've also read that we should only do it once a year and the implication is it damages the remaining lifetime of the batteries.
On the diagnostic tests screen, I see:
Self-Test
Passed on June 29, 2022
Calibration
Not Available on June 28, 2022
In the NMC event log, I see:
Date Time User Event
2022-06-29 18:08:12 Device UPS: Passed a self-test.
2022-06-29 18:07:02 Device UPS: Started a self-test.
2022-06-29 00:06:08 Device UPS: Runtime no longer below selected threshold.
2022-06-28 23:49:05 Device UPS: A low battery condition no longer exists.
2022-06-28 23:49:03 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
2022-06-28 23:48:57 Device UPS: Runtime calibration canceled.
2022-06-28 23:47:52 Device UPS: Runtime below selected threshold.
2022-06-28 23:41:16 Device UPS: Started a runtime calibration.
2022-06-28 12:25:17 Device UPS: Passed a self-test.
2022-06-28 12:24:16 Device UPS: Started a self-test.
2022-06-28 06:10:11 Device UPS: Passed a self-test.
2022-06-28 06:08:59 Device UPS: Started a self-test.
I want the runtime displayed on the UPS to be as accurate as possible. So I'd like to know that runtime cal completed successfully. I reviewed the logs on the lcd display on the front of the symmetra and noted that simple self tests are logged as "On Batt" and then "Self Test Passed". The calibration was logged as: (In Order)
Runtime Cal Started
On Batt
Runtime Below Limit
Runtime Cal Stopped
Low-Battery
Online
Battery Recharged
Runtime Above Limit
The word "stopped" is what I'm not sure about... if it should say 'Passed' perhaps.