Posted: 2022-02-14 10:46 PM
Indications are that derating is a concept that is not well appreciated by all. Consider some real-world scenarios below, i.e. examples pertaining to power distribution at 400V three-phase AC:
What seems to be common to the above scenarios is that when all transformers would supply rated current, this current is about 90% of the nominal ratings of the ACB and main LV busbars. This points to the designer's recognition that derating is to be expected with different environmental conditions, notwithstanding the responsibility to consider a rated diversity factor.
One might reasonably pose some questions: Why are the circuit breakers [and busbars] selected with nominal ratings that exceed the rated transformer secondary currents [?] Are there compelling reasons to select devices with ratings that provide room to manoeuvre?
See the Schneider Electric expert blog to discover more insights on variables impacting derating:
Posted: 2022-02-16 01:41 AM
As a suggestion to provide some insight into this question, consider downloading a circuit breaker catalogue, such as the MasterPact or ComPact NS range catalogues that may be accessed on Schneider Electric website. As an example, see the catalogue at the link: https://www.se.com/ww/en/download/document/LVPED211021EN/. The catalogues typically provide guidance about derating associated with temperature, busbar connection orientation and installation recommendations, etc.