Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82491members
350064posts

SmartConnector Weather Service - step-by-step guide

SmartConnector Forum

Discussion of SmartConnector applications for integration of various other building management systems (BMS) into EcoStruxure Building Operation

Solved
mike_meirovitz
Commander
Commander
0 Likes
7
486

SmartConnector Weather Service - step-by-step guide

Hi,

I am looking for a step-by-step guide that explains how to define the EWS server in the EBO. I am using EBO 3.0.

To be more specific, what should be the values of the following fields?

EWS Server.png

 

Thank you.

Mike

Tags (1)

Accepted Solutions
Nedjma
Community Alumni (Retired)
Community Alumni (Retired)
0 Likes
0
412

Re: SmartConnector Weather Service - step-by-step guide

Hi @mike_meirovitz,

 

@Nick-Iebba helped you to solve your problem. Please click on “Accept as Solution” so other members can find the same solution through the search bar.

 

Thank you!

See Answer In Context

7 Replies 7
Nick-Iebba
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
5
481

Re: SmartConnector Weather Service - step-by-step guide

There is currently no guide (that I know of) that goes over defining the server in EBO; however, it is a quick process.

The address for your EWS server should look something like http://localhost:PORT#/EcoStruxure/DataExchange, or something similar, depends how it was configured in the Processor Configuration.

 

With that in mind, here is what the fields should have:

1. EWS Server: localhost

2. Protocol: HTTP, EWS Communication Port: PORT#

3. EWS Path: EcoStruxure/DataExchange

4. The username and password are whatever was defined for the username and password for the EWS server (this was specified in the configuration of the Setup Processor).

mike_meirovitz
Commander
Commander
0 Likes
4
477

Re: SmartConnector Weather Service - step-by-step guide

Hi Nick,

 

Thank you for your answer. I have followed your steps. When I browse the tree in the EBO, and reach System > Hardware > EcoStruxure Web Services > EcoStruxure Web Service_Weather, I get an error. See below. Any idea what is wrong?

 

Thank you!

Mike

 

Capture.JPG

Nick-Iebba
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
3
474

Re: SmartConnector Weather Service - step-by-step guide

Check the EWS server on the Smart Connector web portal to see if it is running. Assuming you typed in the correct details for the interface, the problem lies with the server having not started.

Go to the server under the EWS Server tab and hit the play icon (although, it should have started upon creation). If it is running, that icon will turn into a square "Stop" icon.

If it does not play, consult the logs under C:\Program Data\SmartConnector\Logs (enable "View hidden items" in Windows Explorer to find the Program Data folder).

mike_meirovitz
Commander
Commander
0 Likes
2
471

Re: SmartConnector Weather Service - step-by-step guide

Hi Nick,

 

The EWS is running. See below.

Capture.JPG

 

See the relevant part of the SmartConnector log file:

2019-12-04 06:52:05.1146,Debug,Service,<no principal>,MayNotContinue : The license you are attempting to use was not created for this machine.,
2019-12-04 06:52:05.2551,Info,WorkerThread,<no principal>,Weather Update Processor,Started,
2019-12-04 06:52:05.2864,Debug,WorkerThread,<no principal>,Weather Update Processor,InstantiateProcessor,ET=31 mSec,
2019-12-04 06:52:05.3645,Debug,WorkerThread,<no principal>,Weather Update Processor,Execute (start),2019-12-04T04:52:05,
2019-12-04 06:52:05.3645,Debug,Processor,<no principal>,Processor Weather Update Processor Execute started,
2019-12-04 06:52:05.5208,Error,Processor,<no principal>,The supplied value is not consistent with the ValueItem's Type property.
at Mongoose.Ews.Server.Data.EwsServerDataAdapter.ModifyValueItemValue(EwsValueItem toModify, Nullable`1 newValue, Nullable`1 newState)
at SmartConnector.WeatherExtension.UpdateProcessor.DoUpdateCurrentConditions(Int64 cityId)
at SmartConnector.WeatherExtension.UpdateProcessor.DoUpdates(Int64 cityId)
at CallSite.Target(Closure , CallSite , UpdateProcessor , Object )
at SmartConnector.WeatherExtension.UpdateProcessor.Execute_Subclass()
at Mongoose.Process.Processor.Execute(CancellationToken token, ProcessorExecutionMode mode)
,["Weather Update Processor"],
2019-12-04 06:52:05.5208,Debug,Processor,<no principal>,Processor Weather Update Processor Execute completed,

 

I see 2 problems:

1. license issue. My SmartConnector license seems to be valid...

2. Error,Processor,<no principal>,The supplied value is not consistent with the ValueItem's Type property. Do you understand what is wrong?

 

Thanks!

Mike

 

 

Nick-Iebba
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
466

Re: SmartConnector Weather Service - step-by-step guide

Interesting. I have only seen this issue as a result of incorrect configuration or a stopped server. Are you following the training and going through the steps to make and deploy the processor yourself?

Unfortunately, the log excerpt you showed me doesn't help; it shows issues with the Update Processor, not the EWS Server. What you would want to do now is turn on EWS Consume Logging. To do this, in the Smart Connector Web portal, go to Setup -> Logging Filters. Also, set logging level to Trace (Setup -> Service Settings).

 

As for the errors you are seeing in the log:

1. I have not had this error before. My assumption is that you created the license incorrectly on SmartConnectorServer.com, or are using a license that someone else made for themselves. If you are indeed following the training, go through the licensing section step-by-step.

2. The update processor is trying to update Int64 CityId with a value that is not of type Int64, this indicates a programming error in the Update Processor.

mike_meirovitz
Commander
Commander
0 Likes
0
460

Re: SmartConnector Weather Service - step-by-step guide

Hi Nick,

 

Thank you for your answer. Logging Level is already set to TraceEws Consume is already set to True.

 

We will check the Update Processor for the CityId variable.

 

Thank you!

 

Mike

Nedjma
Community Alumni (Retired)
Community Alumni (Retired)
0 Likes
0
413

Re: SmartConnector Weather Service - step-by-step guide

Hi @mike_meirovitz,

 

@Nick-Iebba helped you to solve your problem. Please click on “Accept as Solution” so other members can find the same solution through the search bar.

 

Thank you!