Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Relai de chaudière et têtes thermostatiques

Schneider Electric Wiser Forum

Connect with Wiser Smart Home solution experts in the Schneider Electric Wiser forum. Discuss tips on features, updates, installation, and how to get the most out of your Wiser products.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Schneider Electric Wiser
  • Schneider Electric Wiser Forum
  • Re: Relai de chaudière et têtes thermostatiques
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
David_SE
David_SE Mentor
214
Alfred_SE
Alfred_SE Leader
24
Maude.wiser.
Maude.wiser. Contributor
22
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Schneider Electric Wiser Forum
Start a Topic
Solved
jefareussi
jefareussi
Explorer

Posted: ‎2026-09-09 12:11 PM . Last Modified: ‎2026-09-09 12:13 PM

0 Likes
4
265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-09 12:11 PM . Last Modified: ‎2026-09-09 12:13 PM

Relai de chaudière et têtes thermostatiques

Bonjour.

J'ai une installation Wiser avec une passerelle 2ème Gen,

J'ai 9 têtes thermostatiques. Il y a aussi dans le séjour un radiateur sans tête thermostatique, de sorte à toujours avoir un débit d'eau dans le circuit et que seul le séjour soit "pilote" de la pompe à chaleur.

La chauffe se fait par une pompe à chaleur air/eau.

J'ai le relai de chaudière simple 2ème Gen et le thermostat d'ambiance dans le séjour.

Même si la température de consigne du thermostat d'ambiance et dépassée, le relai s'enclenche dès qu'une tête thermostatique s'ouvre.

En gros, il y a presque toujours une tête thermostatique ouverte et donc la pompe à chaleur tourne presque en continu, le radiateur dans le séjour est toujours chaud (et il y fait trop chaud). La consommation s'en ressent.

Mon but est seulement de réguler avec le thermostat d'ambiance la température dans le séjour et que les têtes thermostatiques dans les autres pièces se ferment quand leur température dépasse leur consigne et s'ouvrent quand leur température baisse, comme une installation traditionnelle.

Du coup je suis obligé de continuer à piloter la pompe à chaleur à part avec son thermostat d'ambiance d'origine que je ne peux pas contrôler à distance. Le thermostat d’ambiance et le relai chaudière Wiser ne me servent à rien.

J'ai bien essayé de créer une pièce seule à part avec juste le thermostat d'ambiance et le relai, mais ça n'a rien changé. Le relai est réapparu dans toutes les pièces. Si je le supprime d'une pièce, il disparaît de toutes les pièces.

Y a-t-il une solution pour que le thermostat d'ambiance uniquement pilote le relai chaudière et que les têtes thermostatiques fonctionnent de manière indépendante ( sans provoquer le démarrage de la pompe à chaleur) comme dans une installation traditionnelle ?

C'est un problème pour moi et ça limite l'intérêt de ce système.

Merci d'avance.

 

 

Labels
  • Labels:
  • Temperature Control
  • Tags:
  • english
  • french
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
David_SE
David_SE Mentor
Mentor

Posted: ‎2026-10-14 01:08 AM

0 Likes
0
111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-14 01:08 AM

J'espère vous avoir aidé dans la configuration de votre système. Je ferme ce post, n'hésitez pas à en créer en nouveau et à continuer à partager votre expérience avec Wiser.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
lgo44
lgo44
Troubleshooter

Posted: ‎2026-09-14 10:58 AM

1 Like
1
242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-14 10:58 AM

Pour atteindre set objectif, avec Home Assistant et l'intégration Wiser il existe un mode passif qui permet de specifier quelle entités peuvent solliciter la chaudière , les entités en mode passif ouvrent les vannes thermostatiques sans solliciter le chaudière.

Reply

Link copied. Please paste this link to share this article on your social media post.

jefareussi
jefareussi
Explorer

Posted: ‎2026-09-15 09:47 AM

In response to lgo44
0 Likes
0
221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-15 09:47 AM

Merci beaucoup pour votre réponse.

Malheureusement je n'utilise pas Homes Assistant et je voulais la solution Wiser car elle est plus fiable et peut fonctionner de façon autonome hors connexion.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

David_SE
David_SE Mentor
Mentor

Posted: ‎2026-09-15 10:26 AM . Last Modified: ‎2026-09-15 10:26 AM

0 Likes
0
228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-15 10:26 AM . Last Modified: ‎2026-09-15 10:26 AM

Bonjour  @jefareussi ,

Vous pouvez mettre en oeuvre l'alternative proposée par @lgo44 via Home Assistant.

Avec Wiser home, il est possible de paramétrer indépendamment le chauffage de chacune pièce et de le lier ou non au relais de la chaudière (paramètre "canal" dans la page de la "pièce").

Actuellement, une erreur s'affiche lorsque vous activez ce paramètre, l'équipe travaille à sa résolution mais vous pouvez continuer à contrôler la température de chaque pièce avec les vannes thermostatiques (Wiser ou non).

Une autre alternative (temporaire) est de garder le canal de chacune des pièces sur le relais de chaudière et de créer des programmes indépendants pour chaque pièce avec, par exemple, des consignes de température plus élevées dans la pièce où vous installez le thermostat d'ambiance et des températures légèrement plus faibles dans les autres pièces.

Cordialement.

David

 

Reply

Link copied. Please paste this link to share this article on your social media post.

David_SE
David_SE Mentor
Mentor

Posted: ‎2026-10-14 01:08 AM

0 Likes
0
111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-14 01:08 AM

J'espère vous avoir aidé dans la configuration de votre système. Je ferme ce post, n'hésitez pas à en créer en nouveau et à continuer à partager votre expérience avec Wiser.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore