I replaced a Danfoss wireless stat with a Wiser Gen 1 hub and wireless stat. Over the last 24 hours, the Wiser system has caused the heat pump to turn on roughly 40 times, for 10-14 minutes at a time. Only one period overnight did it remain on for about 5 hours. The hub is configured for "heat pump". Any advice please?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-05 02:12 AM
Hi @StuartA ,
Thanks for your post.
First, please note in the Wiser Gen2 hub, we implement a logic to avoid heat pump cycling. However in Gen 1 this logic is not available but you can apply a workaround.
If, for example, you want your home to be heated at 20°C for a period of time, we suggest to select a higher set point like 22°C for most of that period and to reduce the set point to 18°C for the rest of that period.
Your heat pump being typically less powerful than your former boiler, will require a longer time to heat up your home. By scheduling the HP in that manner, it will run only one cycle for that period of time.
BR
David
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-05 02:12 AM
Hi @StuartA ,
Thanks for your post.
First, please note in the Wiser Gen2 hub, we implement a logic to avoid heat pump cycling. However in Gen 1 this logic is not available but you can apply a workaround.
If, for example, you want your home to be heated at 20°C for a period of time, we suggest to select a higher set point like 22°C for most of that period and to reduce the set point to 18°C for the rest of that period.
Your heat pump being typically less powerful than your former boiler, will require a longer time to heat up your home. By scheduling the HP in that manner, it will run only one cycle for that period of time.
BR
David
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-05 01:56 PM
Thanks David. I have a non smart wireless thermostat and in use with the pump it's not causing much short cycling - we just keep the same temperature 24/7. I'll use this over winter and consider upgrading to the Gen2 hub if I feel that it would benefit us.