Posted: 2025-09-25 11:59 PM
Hello Everyone,
I am selecting Surge Protection Devices for the SCADAPack 470i, but I could not found enough information in the manuals.
I am wondering if anyone has information on the protection levels of the SCADAPack 470i inputs (Power, Analog, Digital...).
I checked the manual Chapter 16 - Specifications (page 148)
The only information is in Chapter 16.7 - Communications (page 154).
On this interface the Protection level is 2 kV.
I am looking for the same information for all interfaces, more precisely for power, analog and digital.
Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-01 07:57 AM
Hello R.B,
The certifications that the SCADAPack 47x | 47xi meet are documented in the datasheet. I've attached a recent copy, though datasheets can be found on our website by navigating to:
-> Products -> Industrial Automation
-> Telemetry & Remote SCADA
-> SCADAPack 47x | 47xi -> Documents
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-01 07:57 AM
Hello R.B,
The certifications that the SCADAPack 47x | 47xi meet are documented in the datasheet. I've attached a recent copy, though datasheets can be found on our website by navigating to:
-> Products -> Industrial Automation
-> Telemetry & Remote SCADA
-> SCADAPack 47x | 47xi -> Documents
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-01 03:37 PM
Dear Joel,
Thank you for your reply.
Sorry I do not have access to this standards, I tried to check online on different sources.
From my understanding the protection can varies depending on the test level.
Here is a summary of what I found.
| Standard | Type of Surge/Transient | Min Test Voltage (kV) |
| IEC 61000-4-2 | Electrostatic Discharge (ESD) | ±2 kV (contact & air) |
| IEC 61000-4-4 | Electrical Fast Transient (EFT/Burst) | 0.5 kV (power/signal lines) |
| IEC 61000-4-5 | Surge (Lightning, switching surge) | 0.5 kV |
| IEC 61000-4-18 | Damped Oscillatory Transient | ~0.5 kV |
| IEC 60255-21 | Surge (protection relay test) | ~1 kV |
On my project we are only going to use Power, Analog and Digital.
If I apply the information according to the standard and take the worst case scenario here his what I got.
| Standard | Power | Analog | Digital |
| IEC 61000-4-2 | 2kV | 2kV | 2kV |
| IEC 61000-4-4 | 0.5kV | 0.5kV | 0.5kV |
| IEC 61000-4-5 | 0.5kV | 0.5kV | 0.5kV |
| IEC 61000-4-18 | 0.5kV | 0.5kV | 0.5kV |
| IEC 60255-21 | 1kV | 1kV | 1kV |
If this is correct I think this is OK.
Best regards,
R.B