When opening a PRJ file I am met with a prompt informing the file has been migrated from an earlier version of Remote Connect. It has blurred the Open Editor button and not allowed me to see the logic.
Is there a way to view files made on older versions in a newer version of RemoteConnect? If not, where can I find older versions of RemoteConnect for download.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-20 09:44 AM . Last Modified: 2025-05-20 09:57 AM
This can be a big issue, and shows why it's important to archive all your projects before upgrading RemoteConnect. The installer does caution users to do this. However, we're past that point now. There are two possible ways to move forward:
1) If you know the version of RemoteConnect the project was created with, you could:
2) Alternately, this method does not require installing the older version:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-16 12:52 AM
I have moved this post to the appropriate forum.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-20 09:44 AM . Last Modified: 2025-05-20 09:57 AM
This can be a big issue, and shows why it's important to archive all your projects before upgrading RemoteConnect. The installer does caution users to do this. However, we're past that point now. There are two possible ways to move forward:
1) If you know the version of RemoteConnect the project was created with, you could:
2) Alternately, this method does not require installing the older version: