Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

RSSI

Remote Operations Forum

Support forum for Schneider Electric SCADA systems, radios and RTUs. From commissioning integration devices and software, to enhancing existing installations or troubleshooting.​

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Remote Operations
  • Remote Operations Forum
  • RSSI
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Joel_Weder
Commander Joel_Weder Commander
34
BevanWeiss
Spock BevanWeiss
19
sbeadle
Spock sbeadle Spock
15
MartinChartrand
Captain MartinChartrand Captain
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Remote Operations Forum
Solved
tharun
Lieutenant tharun
Lieutenant

Posted: ‎2021-10-27 10:31 PM

0 Likes
3
961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-27 10:31 PM

RSSI

Hi all,

          What is a good RSSI for TRIO ER450. Can i have the RSSI classification of the industrial radios.

 

 

Thanks,

Labels
  • Labels:
  • Radio
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Joel_Weder
Commander Joel_Weder Commander
Commander

Posted: ‎2021-10-28 08:34 AM

0 Likes
2
948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-28 08:34 AM

I have attached a data sheet (brochure) for the ER450 radio. As it is obsolete, that datasheet is not available any more on our website. The basic radio sensitivity is -118 dBm for 12 dB SINAD. (see page 5)  But that number is more to compare against voice type radios. The data sensitivity will vary depending on the modulation type used in your radios. That is on page 6, but also here:

 

4800 bps    -111 dBm   NOTE: all measured at 1x10-6 BER (bit error rate)

9600 bps   -110 dBm

19200 bps  -106 dBm

 

For a reasonably reliable link quality, the industry standard is to design for at least 20 dB of fade margin. This is the difference between the radio's sensitivity (at configured data rate) and the predicted or measured signal level. So desired signal level is:

 

4800 bps   -91 dBm or more (less negative)

9600 bps   -90 dBm or more

19200 bps -86 dBm or more

 

I am not sure what you meant by "RSSI classification" If we have not answered this, please reply with clarification of that.

 

Joel Weder
Remote Operations Specialist
Schneider Electric

See Answer In Context

Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Joel_Weder
Commander Joel_Weder Commander
Commander

Posted: ‎2021-10-28 08:34 AM

0 Likes
2
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-28 08:34 AM

I have attached a data sheet (brochure) for the ER450 radio. As it is obsolete, that datasheet is not available any more on our website. The basic radio sensitivity is -118 dBm for 12 dB SINAD. (see page 5)  But that number is more to compare against voice type radios. The data sensitivity will vary depending on the modulation type used in your radios. That is on page 6, but also here:

 

4800 bps    -111 dBm   NOTE: all measured at 1x10-6 BER (bit error rate)

9600 bps   -110 dBm

19200 bps  -106 dBm

 

For a reasonably reliable link quality, the industry standard is to design for at least 20 dB of fade margin. This is the difference between the radio's sensitivity (at configured data rate) and the predicted or measured signal level. So desired signal level is:

 

4800 bps   -91 dBm or more (less negative)

9600 bps   -90 dBm or more

19200 bps -86 dBm or more

 

I am not sure what you meant by "RSSI classification" If we have not answered this, please reply with clarification of that.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

tharun
Lieutenant tharun
Lieutenant

Posted: ‎2021-10-29 03:25 AM

In response to Joel_Weder
0 Likes
1
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-29 03:25 AM

Please list down the RSSI stages (very strong. strong, weak) for trio ER450  as per the attached the image.

 

 

Attachments
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Joel_Weder
Commander Joel_Weder Commander
Commander

Posted: ‎2021-10-29 10:40 AM

In response to tharun
0 Likes
0
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-29 10:40 AM

It's not quite so easy, because I don't know the configured radio data rate, which would tell me the radio's receiver sensitivity at that rate. So I won't give you exact dBm levels at this point. But for each general state, I can say what the approximate Fade Margin will be. You must go back to earlier comments or the ER450 data sheet we have shared, and find the specified data rate, which will tell you the sensitivity for the speed your radios will operate at.

 

Fade Margins: (approximate)

Below 0 dB  No communication

0-9 dB     Very weak

10-19 dB  Weak

20-29 dB  Good

30-39 dB  Very strong

40+ dB     Extremely strong

 

NOTE:  A 0 dB fade margin would occur at the point where the radio is hearing a signal equal to the specified receiver sensitivity in dBm at the over-the-air data rate of the radios.

 

Joel Weder
Remote Operations Specialist
Schneider Electric
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc