Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Saitel DR - can one use VPIS-VO V3 for FPI?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Re: Saitel DR as FPI using VPIS VO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
41
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
neracali
neracali
Contributor

Posted: ‎2025-05-19 12:10 AM . Last Modified: ‎2025-05-21 11:39 PM

0 Likes
7
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-19 12:10 AM

Saitel DR - can one use VPIS-VO V3 for FPI?

Hi community,

 

Is it possible to use VPIS_VO (VPI6261x) as a voltage sensor with Saitel DR AB_AC/LPVT as Fault passage indication module for fault indication/direction and measurement? 

VPIS_VO is by default used with T300 SC150/160-LPVT using wire adapter EMS59577.
Is there any wire adapter for AB_AC/LPVT coax voltage terminals?

 

Thanks!

@Iván_González 

Labels
  • Labels:
  • Saitel range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2025-05-20 11:32 PM

1 Like
0
2616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 11:32 PM

Hello Neracali.

 

On page 73 of the document you attached. Hope this helps you to take the correct decision.

 

JuanRayo_0-1747809002666.png

 

See Answer In Context

Reply
Replies 7
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2025-05-20 12:16 AM

0 Likes
1
2686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 12:16 AM

Hello Neracali.

 

There is no wire adapter to interconnect  VPIS_VO (VPI6261x) with Saitel DR.

Saitel DR like any other member of Saitel´s family has not been designed for protective functions nor for FPI although we participated in an european I+D project with DR working as a FPI (special logical program) and IEC61850-GOOSE as the main driver to interchange information.

Reply
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2025-05-20 01:48 AM . Last Modified: ‎2025-05-20 01:51 AM

0 Likes
1
2674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 01:48 AM

Hello Neracali,
Supporting capacitive dividers is quite unique on the RTU market.

Here are some explanations as to why T300 can support capacitive dividers (i.e., VPIS-VO V3, VDS LRM, VDS HR, PPACS and VDIS) and why Saitel DR CT/VT module can't.
As capacitive dividers are cheap and have a limited footprint, MV switchgear are normally fitted with these (1 unit per MV switch: load break switch, isolating switch, or circuit breaker) to provide a local visual indication of the presence of MV voltage on each of the 3 phases.
However, although a capacitive divider can provide a voltage output, it cannot follow any MV measurement standard: due to that, it cannot be considered as a MV voltage sensor, which is the reason for which it cannot be used with Protection Relays.

Saitel DR CT/VT module was designed for traditional MV voltage sensors (i.e., VTs) but not for capacitive dividers.
PowerLogic T300 is an RTU specialized for MV/LV substations (where customers mostly use capacitive dividers). That is why SC150 switch module has been designed to provide FPI & MV AC measurements, and to support both traditional MV voltage sensors (VTs and LPVTs) and capacitive dividers through an external adapter:

  • EMS59577 for VPIS-VO V3,
  • EMS59570 for VDS LRM or VDIS,
  • EMS59580 for VDS HR,
  • EMS59575 for PPACS

 

BR - Jean-Yves
Reply
neracali
neracali
Contributor

Posted: ‎2025-05-20 02:07 AM

0 Likes
0
2674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 02:07 AM

Thank you @JuanRayo for your answer.

 

In document https://download.schneider-electric.com/files?p_Doc_Ref=SE-M579-USR_EN&p_enDocType=User+guide&p_File... after page 37 Fault Detection Indication function is described. I checked in Easergy Builder that we can add this function and assign database elements.

So my next questions are:
1. what type of LPVT sensors can be used (preferably with Coax connectors)?
2. does some Coax "pigtails" come with ordered AB_AC-LPVT or can be ordered separately?
3. could we use VPI6261x (VPIS_VO) as voltage sensors, connect them somehow to the AB_AC-LPVT module and calibrate (page 66) for Fault Detection Indication function as described in upper document?

BR,

Reply
neracali
neracali
Contributor

Posted: ‎2025-05-20 03:31 AM

0 Likes
0
2655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 03:31 AM

Dear @JYPOC ,

 

I asked about AB_AC-LPVT module, not AB_AC with VT option.
I couldn't find what voltage sensors I can use with it (capacitive or some resistive LP voltage dividers).

Does SE have some in their portfolio and could it be VPIS-VO V3?
This module also supports magnitude and angle calibration (page 66).

So I asked what is adequate voltage sensor to reach described SW function (Fault detection Indication)?

Could you help us @Iván_González , please?

 

BR,


 

Reply
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2025-05-20 07:13 AM

0 Likes
1
2638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 07:13 AM

Hello again Neracali.

The AB_AC LPVT comes with coaxial connectors. In principle, any LPVT with a coaxial connector within the specified range could be connected. The AB_AC does not have coaxial cables, only the fixed connectors soldered to the PCB.

Regarding the VPIS-VO, I can't find any documentation for the sensor on the website. According to the information on the specific adapter for the SC150, it appears to generate a voltage of 1 to 30VAC L-L, which is not compatible. The output connector type is also not coaxial. You would need an adapter that generates the appropriate output voltage and converts to coaxial. There is no such adapter for the T500.

 

Reply
neracali
neracali
Contributor

Posted: ‎2025-05-20 07:46 AM

0 Likes
0
2637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 07:46 AM

Thank you @JuanRayo ,

I found also these details regarding VPIS VO output, but still can't find input characteristics for AB_AC-LPVT.
What is "specified range" for this voltage LPVT input?

I hope that someone will soon publish some post or document regarding sensor product codes that can be used for voltage measurement with AB_AC-LPVT.
Until that it is useless module regarding voltage measurement, synchrocheck, energy meter etc.

Reply
JuanRayo
JuanRayo Mentor
Mentor

Posted: ‎2025-05-20 11:32 PM

1 Like
0
2616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 11:32 PM

Hello Neracali.

 

On page 73 of the document you attached. Hope this helps you to take the correct decision.

 

JuanRayo_0-1747809002666.png

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore