Hi there,
Greetings and hope you are doing well.
I have a customer query asking for seamless redundancy of the substation RTU, where I am proposing PowerLogic T500. The customer specifications says "The devices shall be configured in a primary/backup arrangement, ensuring seamless failover (no interruption to operation) from primary to backup (hot standby) RTU if the primary were to fail."
Could you please help me know -
1 - Does PowerLogic T500 support Seamless Redundant switching?
2 - If not, what is the failover time for the PowerLogic T500 substation RTU?
Thank you and Best Regards,
Kamal Kant
Link copied. Please paste this link to share this article on your social media post.
Hello @Kamal_Kant
Link copied. Please paste this link to share this article on your social media post.
Hello @Kamal_Kant
Link copied. Please paste this link to share this article on your social media post.
Hi @JuanRayo ,
Thank you for the response. Much appreciated. Is there a formula to calculate the switch-over time in Hot or Cold mode of T500? It would help a lot during customer discussions.
Best Regards,
Kamal Kant