Hello All,
I understand that HU280 CPU hold the protocol buffer events in case of SCADA connection failure initially and thereafter power loss/reboot.
However, I would like to know maximum number of events stored in buffer memory per open standard telemetry protocol such as: IEC 61850, IEC 101, IEC 104 and DNP3.
Link copied. Please paste this link to share this article on your social media post.
Hello @DhananjayJamdade
For IEC 61850
Each buffered RCB instance has two circular buffers of 20 kB:
Beware: configurable buffer size is not supported.
How many events can be buffered in 20kB?
To calculate how many events this equates to, we need to consider specific DO types. For example, one SPS DO event in a typical status dataset of 64 SPS DOs. Each entry in the RCB buffer stores:
Therefore a server side BRCB buffer could store approximately 20kB / 42 = 487 such SPS events
For DNP3.0 slave
Buffer size could be configured in Easergy Builder for every Object type like here below:
For IEC 101-104 slave
Buffer size could be configured in Easergy Builder for every point type like here below:
Link copied. Please paste this link to share this article on your social media post.