Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerLogic T300 - When used as a slave IEC 104 device of ABB RTU, why is analog data reading slow?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • Re: PowerLogic T300 - When used as a slave IEC 104 device of ABB RTU, why is analog data reading slow?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
41
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Hoang_Phu
Hoang_Phu
Contributor

Posted: ‎2025-03-28 02:27 AM . Last Modified: ‎2025-05-16 12:16 AM

2 Likes
3
1616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-28 02:27 AM

PowerLogic T300 - When used as a slave IEC 104 device of ABB RTU, why is analog data reading slow?

Hello guys, good day. I have a question for you all. I am reading the analog data of P5 relay from T300 rtu and sending it to ABB rtu via 104 protocol, but the value I am sending is being read very slowly on ABB rtu, maybe changing after 3-5 minutes. The digital value is fine. The analog value that T300 is reading is normal. What settings have I missed?

Labels
  • Labels:
  • Application cases
  • PowerLogic P3
  • PowerLogic P5
  • PowerLogic T300
Tags (5)
  • Tags:
  • english
  • IEC 104
  • p3
  • P5
  • t300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mathieu_Lansoy
Mathieu_Lansoy Mentor
Mentor

Posted: ‎2025-05-15 03:04 AM

1 Like
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 03:04 AM

Hello,

 

The transmission of analogue values using IEC 104 Protocol is linked to different processes:

- the client (here ABB RTU) is sending a "General Interrogation" request to the server (T300). The server will answer with the content of all its IEc104 database (including analogue values). (this can also be done with a specific "read" request to read only some variables). (the period for this request is a setting of the client)

- cyclic analogue events: some elements of the database can also be sent cyclically by the T300 (T300 IEC104 settings. here for example, all "MMEC" variables will be sent cyclicly every 120s)

Mathieu_Lansoy_0-1747302017899.png

 

- spontaneous  events: if a "Threshold" is associated to a analogue variable, a spontaneous event (that can be timestamped) is generated when the gap with the last sent value is higher than the thresold, and sent to the client. The threshold is expressed in absolute value (not in percentage).

Here a threshold of 10(A) is associated to the Phase current, so each time the variation of the current (versus the last sent value) will be higher than 10 A, an event will be transmitted.

Mathieu_Lansoy_0-1747302582949.png

Typically, we are using 10(A) for currents, 1000 (or 1500)(V) for (MV) voltages, 10000 for powers, 5(°) for temperature. But it can be adapted to have more or less events.

 

We don't have the configuration for this project, we can suppose that thresholds are not set on the T300, and cyclic scan neither. So the refresh of analogue values on the client is only due to GI rate. (3 min ?)

Advice: set some thresholds to the analogues values that are shared with the ABB RTU.

(this is done in Easergy Builder / coreDb : Analog tab / Destinationx Threshold)

 

Regards,

 

  Mathieu.

 

 

See Answer In Context

Reply
Replies 3
Araceli_Monje
Araceli_Monje Mentor
Mentor

Posted: ‎2025-05-15 02:23 AM

0 Likes
0
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 02:23 AM

@Mathieu_Lansoy , hi, could you please support with this question?, thx.

Reply
Mathieu_Lansoy
Mathieu_Lansoy Mentor
Mentor

Posted: ‎2025-05-15 03:04 AM

1 Like
0
1532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 03:04 AM

Hello,

 

The transmission of analogue values using IEC 104 Protocol is linked to different processes:

- the client (here ABB RTU) is sending a "General Interrogation" request to the server (T300). The server will answer with the content of all its IEc104 database (including analogue values). (this can also be done with a specific "read" request to read only some variables). (the period for this request is a setting of the client)

- cyclic analogue events: some elements of the database can also be sent cyclically by the T300 (T300 IEC104 settings. here for example, all "MMEC" variables will be sent cyclicly every 120s)

Mathieu_Lansoy_0-1747302017899.png

 

- spontaneous  events: if a "Threshold" is associated to a analogue variable, a spontaneous event (that can be timestamped) is generated when the gap with the last sent value is higher than the thresold, and sent to the client. The threshold is expressed in absolute value (not in percentage).

Here a threshold of 10(A) is associated to the Phase current, so each time the variation of the current (versus the last sent value) will be higher than 10 A, an event will be transmitted.

Mathieu_Lansoy_0-1747302582949.png

Typically, we are using 10(A) for currents, 1000 (or 1500)(V) for (MV) voltages, 10000 for powers, 5(°) for temperature. But it can be adapted to have more or less events.

 

We don't have the configuration for this project, we can suppose that thresholds are not set on the T300, and cyclic scan neither. So the refresh of analogue values on the client is only due to GI rate. (3 min ?)

Advice: set some thresholds to the analogues values that are shared with the ABB RTU.

(this is done in Easergy Builder / coreDb : Analog tab / Destinationx Threshold)

 

Regards,

 

  Mathieu.

 

 

Reply
JYPOC
JYPOC Mentor
Mentor

Posted: ‎2025-05-16 12:22 AM . Last Modified: ‎2025-05-16 12:24 AM

0 Likes
0
1501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-16 12:22 AM

Hello @Hoang_Phu 

Your guess was correct, the issue you meet is solved by setting IEC 104 parameters accordingly.

As indicated by Mathieu, you can either do it on the ABB RTU (make a faster general interrogation) or change settings on T300: which one have you chosen?

Once you have implemented it and verified all is well, please mark Mathieu's proposal as a solution.

Regards

BR - Jean-Yves
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore