Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

PowerLogic T300 - IEC 61850 connection error to P3?

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - IEC 61850 connection error to P3?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Lt. Commander Araceli_Monje Lt. Commander
23
HenriGRASSET
Captain HenriGRASSET Captain
14
Rudolf_Simon
Commander Rudolf_Simon Commander
13
View All
Related Products
product field
Schneider Electric
PowerLogic T300
product field
PowerLogic
PowerLogic P3

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Solved
elnur
Crewman elnur
Crewman

Posted: ‎2025-01-28 09:22 AM . Last Modified: ‎2025-01-31 01:22 AM

0 Likes
11
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-28 09:22 AM

PowerLogic T300 - IEC 61850 connection error to P3?

T300 connected to P3 via 61850

Dear colleagues.

 

I receive conf error message when try to connect P3U to T300 via 61850. I configure 61850 server using Build SCD option in Easergy Builder and download created conf file into T300 . The question is why I receive error message from T300 if all the configuration done by Easergy Builder? I did not touch anything after creating the file. On this stage there is no any points or client connection defined. Please see below pic.

Can you share step by step instruction how to configure  P3-> T300 connection via 61850?

Thanks in advance,

 

elnur_0-1738084852223.png

 

 

 

elnur_1-1738084852214.png

 

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
  • Thumbnail of PowerLogic P3
    PowerLogic
    PowerLogic P3
View products (2)
Labels
  • Labels:
  • IEC61850
  • PowerLogic P3
  • PowerLogic T300
Tags (4)
  • Tags:
  • english
  • iec 61850
  • PowerLogic P3
  • PowerLogic T300
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2025-02-06 01:15 AM

0 Likes
1
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-06 01:15 AM

Hello Elnur.

The firmware version you got v1.2.2 is very old. Take into account that 61850 controller is active in T300 since release 1.3.1 so you need to upgrade it.

 

Please contact your Front office or my colleague Mathieu Lansoy for this.

See Answer In Context

Reply
Replies 11
elnur
Crewman elnur
Crewman

Posted: ‎2025-01-29 09:58 AM

0 Likes
0
1119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-29 09:58 AM

Just for better understanding, I have just added IEC61850 server in Easergy Builder choosing Build SCD option. Then not touching anything downloaded the configuration into T300 and receive error in the picture, Why there is error message if all configurations done by Easergy Builder? I mean on this stage there is no any points  or client connection defined but T300 warm about configuration error.   

Reply
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2025-01-30 11:53 PM

0 Likes
1
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-30 11:53 PM

Hello Elnur. Just to my have a clear picture in mind, if you want to integrate P3U in T300 you must have P3U´s cid file to configure T300 as a client, Is that correct?... if so the option "Build SCD" is correct as a first step but then you must import the cid file and start the process to integrate the device itself within T300 configuration. I have prepared a brief summary with the steps to be taken for this. I wish it helps you

Attachments
Reply
TomBerry
Lieutenant JG TomBerry Lieutenant JG
Lieutenant JG

Posted: ‎2025-01-31 12:13 AM

0 Likes
1
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-31 12:13 AM

To see the reason why the T300 rejected the configuration, look at the T300 (HU250) system log.

Reply
JYPOC
Commander JYPOC Commander
Commander

Posted: ‎2025-01-31 01:27 AM

0 Likes
1
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-31 01:27 AM

Hello Elnur, as you can see from this old post (https://community.se.com/t5/PAE-Protection-Relays-Controllers/Easergy-T300-Easergy-P3-and-IEC-61850-...), the IEC 61850 connection of PowerLogic T300 to multiple PowerLogic P3 has already been successfully performed quite some time ago.

BR - Jean-Yves
Reply
elnur
Crewman elnur
Crewman

Posted: ‎2025-02-02 02:33 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-02 02:33 AM

Hello Juan,

 

thnka you for your help. I did exactly how you propsed and still tehre is an error message. i have cheked inlog ifle and there isonly one error as below:

02/02/2025 14:25:58.049 ERRO Rdb:contManGo: sorry, no way to start i61sc controller. No exe file found
 
does it mean that i have to download some exe file into T300??? Or this file shoudl be in some directory of easergy builder? 
Reply
elnur
Crewman elnur
Crewman

Posted: ‎2025-02-02 03:01 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-02 03:01 AM

Hello JYPOC ,

 

i do not have acess to link you shared. How can get this acess?

Reply
elnur
Crewman elnur
Crewman

Posted: ‎2025-02-02 03:14 AM

0 Likes
0
1051
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-02 03:14 AM

Hello Tom,

only tehre is only one error message as below"

 

ERROR db:contManGo: sorry, no way to start i61sc controller. No exe file found

 

Reply
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2025-02-03 12:01 AM

0 Likes
1
1041
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-03 12:01 AM

Hello Elnur. Let us know the firmware version loaded (perhaps you need to upgrade it) and also share with us the configuration files 

Reply
elnur
Crewman elnur
Crewman

Posted: ‎2025-02-04 08:56 AM

0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-04 08:56 AM

Hello Juan,

 

please find attached conf file and screenshot with firmware (1.2.2-6224) below. I was thinking to upgrade the firmware but could not find proper file.

 

elnur_0-1738687983232.png

 

Attachments
conf.tar.7z
Reply
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2025-02-06 01:15 AM

0 Likes
1
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-06 01:15 AM

Hello Elnur.

The firmware version you got v1.2.2 is very old. Take into account that 61850 controller is active in T300 since release 1.3.1 so you need to upgrade it.

 

Please contact your Front office or my colleague Mathieu Lansoy for this.

Reply
elnur
Crewman elnur
Crewman

Posted: ‎2025-02-09 10:00 PM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-09 10:00 PM

Hello Juan, thank you for support, I have updated the firmware and everything is good now. 

Thanks for all team for the help.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of