Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerLogic T300 - How to configure the ATS GEN function

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • PowerLogic T300 - How to configure the ATS GEN function
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Araceli_Monje Mentor
74
JuanRayo
JuanRayo Mentor
38
Arun-kumar_PS
Arun-kumar_PS Mentor
33
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic T300

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Ray_Chang_EPEC
Ray_Chang_EPEC
Contributor

Posted: ‎2022-12-26 12:33 AM . Last Modified: ‎2025-05-26 12:33 AM

0 Likes
2
3391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-26 12:33 AM

PowerLogic T300 - How to configure the ATS GEN function

Hi:

 

  This is the first time that we are setting up a T300 system. We want to use T300-ATS for a standby generator system. 

  • Self-return mode will be our choice: but we can't find where this mode can be set.
  • We try to use HU250's digital output to start the generator: it this possible?
  • We got a setting for this system but can't find all what is needed to set a value.
  • Where can I find a reference for typical T300-ATS setting?

Thanks if anyone can help on first time setting.

   

   

  • Thumbnail of PowerLogic T300
    Schneider Electric
    PowerLogic T300
View products (1)
Labels
  • Labels:
  • PowerLogic T300
Tags (5)
  • Tags:
  • english
  • PowerLogic T300
  • t300
  • T300 ATS
  • T300 GEN
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jean-luc_batard
jean-luc_batard Troubleshooter
Troubleshooter

Posted: ‎2023-01-02 08:26 AM

0 Likes
0
3388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-02 08:26 AM

Hi Ray

 

Yes Easergy T300 provides Automatic source transfer functionality, including selection of return mode

 

 

Here is the corresponding setting as described in User's manual

 

"Allow back to normal source" p 144 and detailed on page 148. Select "YES" in your case

"Controls the behaviour after a transfer to the backup source and
voltage returns on the normal source.
"No" means that the ATS waits for voltage absence on the backup
source.
"Yes" means that the system transfers back to the normal source.
"Use a variable" means that back to normal is enabled depending on the
value of a variable (coordinate AATS_BLK_SELF_RE
T)"

 

 

Note that native automatism is meant to manage 2 normal/backup sources.
It may be easily adapted to manage a normal source and a generator
For this follow attached application note

Jean-Luc BATARD
Distribution Automation Senior Application Engineer

See Answer In Context

Attachments
Reply
Replies 2
jean-luc_batard
jean-luc_batard Troubleshooter
Troubleshooter

Posted: ‎2023-01-02 08:26 AM

0 Likes
0
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-02 08:26 AM

Hi Ray

 

Yes Easergy T300 provides Automatic source transfer functionality, including selection of return mode

 

 

Here is the corresponding setting as described in User's manual

 

"Allow back to normal source" p 144 and detailed on page 148. Select "YES" in your case

"Controls the behaviour after a transfer to the backup source and
voltage returns on the normal source.
"No" means that the ATS waits for voltage absence on the backup
source.
"Yes" means that the system transfers back to the normal source.
"Use a variable" means that back to normal is enabled depending on the
value of a variable (coordinate AATS_BLK_SELF_RE
T)"

 

 

Note that native automatism is meant to manage 2 normal/backup sources.
It may be easily adapted to manage a normal source and a generator
For this follow attached application note

Jean-Luc BATARD
Distribution Automation Senior Application Engineer
Attachments
Reply
Ray_Chang_EPEC
Ray_Chang_EPEC
Contributor

Posted: ‎2023-01-02 11:53 PM

0 Likes
0
3383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-02 11:53 PM

Hi @jean-luc_batard :

 

    Thanks for the document. We'll check for detail.

    One more question is does the ATS setting in T300 by default?

    Or i need to add in like this video by Easergy Builder? 
    https://www.youtube.com/watch?v=lPYYkBbsWVU

    I did see some set up need to be added by Easergy Builder in document.

    Cause we don't have any experience on Easergy Builder.

    We may have to check how to use Easergy Builder first or

    We can set by Web on T300 if the ATS setting is in T300 by default.   

 

    Many thanks

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore