Hi. I have a P5U20 that I want to integrate to a CompactLogix PLC over ethernet . How do I go about this?
Link copied. Please paste this link to share this article on your social media post.
Hello @Dahhoodd,
CompactLogix PLC is coming Rockwell Automation, in history P5 has been integrated with CompactLogix 1756-L85EP successfully on customer site using EtherNet\IP protocol. The EDS file generated by P5 can be imported into Rockwell studio 5000 well.
But please note that when make data points configuration there is alignment rule shall be followed as the coming manual below.
Please let me know whether there is any question further.
more example are below:
- For a 2-byte data type, the offset must be a multiple of 2.
- For a 4-byte data type, the offset must be a multiple of 4.
- no rules for a 1-byte data type.
BR
Shaogang from P5 design team
Link copied. Please paste this link to share this article on your social media post.
Hello,P5U20 can support ethernet IP ,MODBUS TCP and IEC61850 protocol. select the proper protocol to communication with PLC.
Link copied. Please paste this link to share this article on your social media post.
Hello @Dahhoodd,
CompactLogix PLC is coming Rockwell Automation, in history P5 has been integrated with CompactLogix 1756-L85EP successfully on customer site using EtherNet\IP protocol. The EDS file generated by P5 can be imported into Rockwell studio 5000 well.
But please note that when make data points configuration there is alignment rule shall be followed as the coming manual below.
Please let me know whether there is any question further.
more example are below:
- For a 2-byte data type, the offset must be a multiple of 2.
- For a 4-byte data type, the offset must be a multiple of 4.
- no rules for a 1-byte data type.
BR
Shaogang from P5 design team