Hi,
For PowerLogic P3F30 relays.
Does anyone know how to put OC1PTOC1$ST$Mod data in a data set in .cid File (for IEC61850),
In exported data set from the relay there is only $str and $op data.
Best regards,
Link copied. Please paste this link to share this article on your social media post.
Hi @Ivan_Puškaš_EC @Araceli_Monje ,
Right click on Data set to modify the dataset which open a window as shown below . search the signal which you want to add to the data set and save the CID file .
Regards,
Ravi Teja
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi @Ivan_Puškaš_EC @Araceli_Monje ,
Right click on Data set to modify the dataset which open a window as shown below . search the signal which you want to add to the data set and save the CID file .
Regards,