Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Micom P122 relay is continuously displaying Hardware alarm Auxiliary power supply 1/1 and not getting reset.
Please suggest how to resolve the issue.
Link copied. Please paste this link to share this article on your social media post.
Hello @Harikrishna1980
This alarm is caused by failure of a optocoupler in the power supply module. This is major alarm and results in blocking of protection and automation function.
The device must be sent to the MiCOM repair center in your country/region for rectification. Please contact your local Schneider representative.
Regards,
Arun
Link copied. Please paste this link to share this article on your social media post.
@Arun-kumar_PS , @Nathalie_Dunand , could your teams please support with this question or guide @Harikrishna1980 to the person that is able to help?, thx.
Link copied. Please paste this link to share this article on your social media post.
Hello @Harikrishna1980
This alarm is caused by failure of a optocoupler in the power supply module. This is major alarm and results in blocking of protection and automation function.
The device must be sent to the MiCOM repair center in your country/region for rectification. Please contact your local Schneider representative.
Regards,
Arun
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.