MiCOM P242 IEC870-5-103

Protection & Control

Schneider Electric support forum about Protection Relays, Substation Controllers & RTUs, Arc Flash Devices & Systems in Medium Voltage and Low Voltage. A place to get support on product selection, installation, commissioning and troubleshooting.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Protection & Control
  • MiCOM P242 IEC870-5-103
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Araceli_Monje
Commander Araceli_Monje Commander
43
Arun-kumar_PS
Commander Arun-kumar_PS Commander
21
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Protection & Control
Start a Topic
Solved
Benjamin4
Benjamin4
Cadet

Posted: ‎2025-11-11 06:57 AM

0 Likes
2
156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-11 06:57 AM

MiCOM P242 IEC870-5-103

Hello,

 

I have a question regarding P242 IEC870-5-103 addresses. I've downloaded the relay database excel file and I'm curious what does it mean in the table when there isn't a "star" in the model number column, does that mean that that address doesn't exist for the relay to send? I'm attaching an image with example. For signal DDB_ANY_TRIP there is a "star" and fothe DB_MIN_F_1_START doesn not. How can I send the second signal to RTU? Also what does the column GI mean ?

example.jpg

Labels
  • Labels:
  • MiCOM range
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arun-kumar_PS
Commander Arun-kumar_PS Commander
Commander

Posted: ‎2025-11-24 11:38 PM

1 Like
1
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 11:38 PM

Hello @Benjamin4 

Yes, your understanding is right. When there isn't a "star" in the model number column, that address doesn't exist for the relay to send. You have to workaround to send the DB_MIN_F_1_START information, like mapping it to the IEC 103 available output signal (output relay/alarm DDB). 

 

The field GI indicates whether the information is included in the general interrogation. For these
INFORMATION NUMBERs both status changes (‘OFF’ to ‘ON’ and ‘ON’ to ‘OFF’) are also transmitted
spontaneously. For the other INFORMATION NUMBERs only the status changes ‘OFF’ to ‘ON’ are
transmitted.

 

See Answer In Context

Reply
Replies 2
Arun-kumar_PS
Commander Arun-kumar_PS Commander
Commander

Posted: ‎2025-11-24 11:38 PM

1 Like
1
74
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 11:38 PM

Hello @Benjamin4 

Yes, your understanding is right. When there isn't a "star" in the model number column, that address doesn't exist for the relay to send. You have to workaround to send the DB_MIN_F_1_START information, like mapping it to the IEC 103 available output signal (output relay/alarm DDB). 

 

The field GI indicates whether the information is included in the general interrogation. For these
INFORMATION NUMBERs both status changes (‘OFF’ to ‘ON’ and ‘ON’ to ‘OFF’) are also transmitted
spontaneously. For the other INFORMATION NUMBERs only the status changes ‘OFF’ to ‘ON’ are
transmitted.

 

Reply
Benjamin4
Benjamin4
Cadet

Posted: ‎2025-11-24 11:53 PM

0 Likes
0
67
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-11-24 11:53 PM

Hello @Arun-kumar_PS 

Thank you very much for the information!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore