I tried to enable Easergy P5 Protection Relay Virtual Inhections in Esetup Pro, but it doesn't work.
May I know the cause and action?
Best Regards.
Link copied. Please paste this link to share this article on your social media post.
Hello @Hyeontae-Song , hello @CCM ,
Please refer to the history solution as link below.
https://community.se.com/t5/PAE-Protection-Relays-Controllers/P5-Virtual-injections-error/m-p/435732
Link copied. Please paste this link to share this article on your social media post.
Well, just to reply to this because i faced the same problem
- first, i tried from ethernet connection and in manual, it said "local connection is mandatory"
- then i tried to use from virtual machine and look like my company windows policy blocked it (compability problem with winpcap..
finally, i used a clear computer out of the company network and virtual injection worked...
Link copied. Please paste this link to share this article on your social media post.
Hello @Hyeontae-Song , hello @CCM ,
Please refer to the history solution as link below.
https://community.se.com/t5/PAE-Protection-Relays-Controllers/P5-Virtual-injections-error/m-p/435732