I want to change the network protocol settings in the P345 relay, but cannot find the ETH COMM mode option in the system data while accessing via relay HMI. Please guide me How I can change the network Protocol settings in the P345 relay.
Relay model number – P34531JA6M0368K @network
Link copied. Please paste this link to share this article on your social media post.
Hello @Jay_CRP12
The parameter ‘ETH COMM mode’ is not available on device P34531JA6M0368K.
In hardware ‘K’, the COMM mode is fixed and determined by the order details. The given model number supports communication mode RSTP.
The flexible COMM mode functionality is available in hardware version ‘M’.