BMS Control of NSX MCCB's Fitted With Communicating Motors

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
5
434

BMS Control of NSX MCCB's Fitted With Communicating Motors

Good morning,

Is there a white paper/information details available on how to control NSX MCCB's which are fitted with communicating motor operators by the BMS/SCADA system?

We are seeing a number of projects which are requiring load shedding/re-close of devices by the BMS/SCADA system and it would appear to be a lot simpler to control this via either RS485 or TCP/IP connection than traditional wired I/O points.  

Tags (1)

Accepted Solutions
Gregoire_Brun
Lt. Commander Lt. Commander
Lt. Commander

Re: BMS Control of NSX MCCB's Fitted With Communicating Motors

Hello Peter

You can find all information about Circuit Breakers With Communicating Motor Mechanism on this document page 56

 

BSCM and NSX cord are needed and you must to pass true communication devices from Enelin'X function to connect it to a Scada (see Page 149  on compact NSX catalogue)

 

 

 

 

 

See Answer In Context

Tags (1)
5 Replies 5
Gregoire_Brun
Lt. Commander Lt. Commander
Lt. Commander

Re: BMS Control of NSX MCCB's Fitted With Communicating Motors

Hello Peter

You can find all information about Circuit Breakers With Communicating Motor Mechanism on this document page 56

 

BSCM and NSX cord are needed and you must to pass true communication devices from Enelin'X function to connect it to a Scada (see Page 149  on compact NSX catalogue)

 

 

 

 

 

Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Re: BMS Control of NSX MCCB's Fitted With Communicating Motors

Thank you Gregoire, that is a great help.

 

Just need to convince consultants now that it can be done...

 

Best regards,

 

Peter Hall.

Tags (1)
Gregoire_Brun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
392

Re: BMS Control of NSX MCCB's Fitted With Communicating Motors

We imagine to create for the futur a 24v DC version for communicative Motor mechanism, should be a needed for you ? 

Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
1
387

Re: BMS Control of NSX MCCB's Fitted With Communicating Motors

That could be interesting.

 

Although we are seeing enquiries at present that open the MCCB's on loss of supply to the busbars. Therefore a 230VAC UVR is needed. If a 230VAC UVR is used it would be quite simple to supply the motor from this supply.

 

A 24VDC option would need a separate DC supply bringing into the panel as the ULP supply could not be used as it is limited in its rating. 

 

A tricky one. On one hand it would be convenient, but in this application maybe the 230V supply is just as convenient?

Tags (1)
Gregoire_Brun
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
370

Re: BMS Control of NSX MCCB's Fitted With Communicating Motors

You are right,

It depend if they use micrologic 5-6-7 with external DC Supply or not.

Tags (1)