Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84589members
353855posts

63A 8P Switch Disconnector

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

63A 8P Switch Disconnector

Can anyone please give me the part number for an 8P 63A disconnector? I'm looking at using one for a bypass on a change over panel.

Tags (1)

Accepted Solutions
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: 63A 8P Switch Disconnector

Hi @RHH-Eltechna ,

 

The request seems to be a 8P switch, not a manual transfer switch (I-O-II). I am interested to understand the application need, let's wait for the information.

 

Christian

See Answer In Context

Tags (1)
9 Replies 9
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: 63A 8P Switch Disconnector

Hello @Peter_Hall ,

 

I attached the Schneider Electric Transferpact catalogue in PDF.
You can use accessoiries like; mechanical interlocking - for devices with extended rotary handle - 40...160 A 

All is described in the PDF attached.

Hope this is of any help!



 


Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Attachments
Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
6
850

Re: 63A 8P Switch Disconnector

Hi @RHH-Eltechna,

 

Thank you for your reply. That one will do for one switch. however, it was the wrap around switch for the mains supply that i was looking for. This needs to be an 8 pole gang operated switch 2 position.

Tags (1)
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: 63A 8P Switch Disconnector

Hi @Peter_Hall ,

 

Sorry, probably my english but I don't understand your need. Could you please post a schematic ?

 

Thanks,

Christian

Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
4
785

Re: 63A 8P Switch Disconnector

Hi @Christian_Bach,

 

No problems. It is though very simple. the unit needs to be as:

 

8 poles.

2 position (off/on).

Single central operating handle.

Tags (1)
Christian_Bach
Lieutenant Lieutenant
Lieutenant
0 Likes
0
770

Re: 63A 8P Switch Disconnector

Hi @Peter_Hall ,

 

Thanks, so basic switch with 8P operated by a single actuator.

 

I am investigating with my colleagues from final distribution products, would a toggle type actuator fit your need ?

 

Would it be possible to share your Bypass schematics (even in private message) ?

 

Thanks,

Christian

 

Tags (1)
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master
0 Likes
2
769

Re: 63A 8P Switch Disconnector

I think I know what you mean, the most common (8P) is 1-0-2 though.

 

Like the jpg files I attached to this post. Coming from our workshop.



Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Attachments
Tags (1)
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: 63A 8P Switch Disconnector

Hi @RHH-Eltechna ,

 

The request seems to be a 8P switch, not a manual transfer switch (I-O-II). I am interested to understand the application need, let's wait for the information.

 

Christian

Tags (1)
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: 63A 8P Switch Disconnector

@Christian_Bach ,

 

Yes, indeed.
Curious we are 🙂




Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Tags (1)
Berkhof
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Re: 63A 8P Switch Disconnector

Hi @Peter_Hall ,

 

Maybe 2x NSXna with a MN coil will do the trick? ( 2x C114100LS 2x LV426806 )

 

Connect the Q1 MN coil to Q2 and the Q2 MN coil to Q1.

 

As soon u switch one of the to breakers open than the other one will disconnect aswell.

 

Closing the 2 breakers will be a 2 handed operation. or with a bypass on the MN coils.

 

Kind regards,

 

John

 

 

 

Tags (1)