63A 8P Switch Disconnector

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

63A 8P Switch Disconnector

Can anyone please give me the part number for an 8P 63A disconnector? I'm looking at using one for a bypass on a change over panel.

Tags (1)

Accepted Solutions
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: 63A 8P Switch Disconnector

Hi @RHH-Eltechna ,

 

The request seems to be a 8P switch, not a manual transfer switch (I-O-II). I am interested to understand the application need, let's wait for the information.

 

Christian

See Answer In Context

Tags (1)
9 Replies 9
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: 63A 8P Switch Disconnector

Hello @Peter_Hall ,

 

I attached the Schneider Electric Transferpact catalogue in PDF.
You can use accessoiries like; mechanical interlocking - for devices with extended rotary handle - 40...160 A 

All is described in the PDF attached.

Hope this is of any help!



 


Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Attachments
Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
6
853

Re: 63A 8P Switch Disconnector

Hi @RHH-Eltechna,

 

Thank you for your reply. That one will do for one switch. however, it was the wrap around switch for the mains supply that i was looking for. This needs to be an 8 pole gang operated switch 2 position.

Tags (1)
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: 63A 8P Switch Disconnector

Hi @Peter_Hall ,

 

Sorry, probably my english but I don't understand your need. Could you please post a schematic ?

 

Thanks,

Christian

Tags (1)
Peter_Hall
Lt. Commander | EcoXpert Master Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master
0 Likes
4
788

Re: 63A 8P Switch Disconnector

Hi @Christian_Bach,

 

No problems. It is though very simple. the unit needs to be as:

 

8 poles.

2 position (off/on).

Single central operating handle.

Tags (1)
Christian_Bach
Lieutenant Lieutenant
Lieutenant
0 Likes
0
773

Re: 63A 8P Switch Disconnector

Hi @Peter_Hall ,

 

Thanks, so basic switch with 8P operated by a single actuator.

 

I am investigating with my colleagues from final distribution products, would a toggle type actuator fit your need ?

 

Would it be possible to share your Bypass schematics (even in private message) ?

 

Thanks,

Christian

 

Tags (1)
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master
0 Likes
2
772

Re: 63A 8P Switch Disconnector

I think I know what you mean, the most common (8P) is 1-0-2 though.

 

Like the jpg files I attached to this post. Coming from our workshop.



Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Attachments
Tags (1)
Christian_Bach
Lieutenant Lieutenant
Lieutenant

Re: 63A 8P Switch Disconnector

Hi @RHH-Eltechna ,

 

The request seems to be a 8P switch, not a manual transfer switch (I-O-II). I am interested to understand the application need, let's wait for the information.

 

Christian

Tags (1)
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: 63A 8P Switch Disconnector

@Christian_Bach ,

 

Yes, indeed.
Curious we are 🙂




Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Tags (1)
Berkhof
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Re: 63A 8P Switch Disconnector

Hi @Peter_Hall ,

 

Maybe 2x NSXna with a MN coil will do the trick? ( 2x C114100LS 2x LV426806 )

 

Connect the Q1 MN coil to Q2 and the Q2 MN coil to Q1.

 

As soon u switch one of the to breakers open than the other one will disconnect aswell.

 

Closing the 2 breakers will be a 2 handed operation. or with a bypass on the MN coils.

 

Kind regards,

 

John

 

 

 

Tags (1)