Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84587members
353854posts

Bagaiman Cara Pengisian Parameter PID

PLC Club Indonesia

Wadah diskusi seputar PLC,HMI, SCADA dan semua hal seputar otomasi pada proses industri, baik mengenai hal teknis, informasi terbaru dan juga seputar bisnis. Forum ini terbuka unutuk semua system integrator industrial di Indonesia

gwynbleidd
Crewman
Crewman
0 Likes
1
388

Bagaiman Cara Pengisian Parameter PID

Bagaimana cara mengisi Kp, Ti, Td pada PID?

misal paramater yang dapatkan Kp=20, Ti=90, Td=45 bagaimana memasukkan ke dalam %MWxx nya apakah perlu dikali dulu? 

Mohon bantuannya, Terima kasih.Screenshot 2021-08-16 181005.png

Tags (2)
1 Reply 1
endr0kho
Crewman Crewman
Crewman
0 Likes
0
346

Re: Bagaiman Cara Pengisian Parameter PID

Tidak perlu dikali, tanda x dimanual tersebut mewakili satuannya, jadi kalau kita masukkan Kp = 10 artinya dalam kalkulasi PID yang dihitung adalah 10x0,01s = 0,1s. begitu juga untuk Ti dan Td

CMIIW

Tags (1)