Is there an easy way to reduce the incident energy on a Service Entrance Swbd.

NEMA Engineers & Designers Forum

A community for the free exchange of ideas and information related to engineers, specifiers and designers within USA and Canada or those who design with North American products.

Solved
JLStanton
Cadet
Cadet
0 Likes
1
450

Is there an easy way to reduce the incident energy on a Service Entrance Swbd.

One of the easiest ways to reduce Incident energy of down stream Distribution on a Service Entrance Swbd, is to separate the Main Disconnect from the rest of the lineup. 

 

If the Main has bottom incoming and top outgoing lugs, you can provide a Top Hat above the Main Section.  On the Distribution Section, you can provide incoming top Lugs with a Top Hat above the incoming Lug Section, then conduit across to connect the two lineups.  I would use some type of fire barrier sealant to make sure the arch can not propagate between the two sections.

 

Even if you separate the two lineups by a foot, the Distribution is no longer dangerous, and if you employ a Maintenance Switch on the Main, you could reduce the Incident energy considerably.  

 

 

 

Attachments
Tags (1)

Accepted Solutions
LouisDamico
Lieutenant Lieutenant
Lieutenant
0 Likes
0
400

RE: Is there an easy way to reduce the incident energy on a Service Entrance Swbd.

Thanks for the helpful information @JLStanton !

See Answer In Context

Tags (1)
1 Reply 1
LouisDamico
Lieutenant Lieutenant
Lieutenant
0 Likes
0
401

RE: Is there an easy way to reduce the incident energy on a Service Entrance Swbd.

Thanks for the helpful information @JLStanton !

Tags (1)