Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Online edits of M340 program from Control Expert

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Re: Online edits of M340 program from Control Expert
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
jerrybenny18
jerrybenny18
Explorer

Posted: ‎2026-05-01 06:29 AM

0 Likes
3
1069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-01 06:29 AM

Online edits of M340 program from Control Expert

Hi, I'm new to programming M340 controllers - my background is in Rockwell. I was wondering if there is an equivalent to "online edits" as we have in Rockwell - i.e making changes to the program without needing to stop the processor.

From my experience so far, if you want to do this in control expert, you have to be online to the PLC first, then make the changes and click "Build Changes" under the "Build" menu. Is this the only way to do it? This seems like if I made changes in an offline copy, that necessitates a PLC download even if it is only changing a few lines of logic? 

Labels
  • Labels:
  • 01. Modicon M340 PAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Trinxs1
Trinxs1 Leader
Leader

Posted: ‎2026-05-04 04:41 PM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-04 04:41 PM

JerryBenny18 online changes are made in the way you have described.  There is also a virtual connect mode where you can make changes (but only those that can be made online) to the project offline.  Reconnect as equal and then build online.  
In both cases however there are changes that require a rebuild all.  In this case you must stop the processor to undertake a full download.

Trial and error with the offline mode is the best way to detect which changes require a rebuild all.  In this case when a change is made open the PLC Build menu to see what options are available.  If only the "rebuild all" is available, then you must stop the PLC for a full download. 
In the virtual connect mode the build changes option should only be undertaken when online.  As soon as build or rebuild all is undertaken the projects are no longer equal.

Trinxs
Senior Technical Sales Consultant - PAC

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
dnordenberg1
dnordenberg1
Contributor

Posted: ‎2026-05-01 11:25 PM

0 Likes
0
1058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-01 11:25 PM

You don't need to be online while you edit and "Build" is the "online change". Just don't click Build while offline because that builds a new version of the program on your computer and it will now differ from the PLC when going online so it doesn't have the current program to compare the changes to any more. Some actions like changing settings and IO configuration can't be done with a online change, if you try to edit something of that Control Expert will warn you that you will need to build offline and then do a full download.

 

If you happen to hit build while offline and you done a lots of changes you don't want to lose, you can export your new program, upload a new copy from the PLC (if upload hasn't been disabled, it is normally allowed) and import your exported changes back over the uploaded project and then you have the current "compiled" project still preserved on your computer. You normally don't need to worry about how big the online changes are.

Reply

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Trinxs1 Leader
Leader

Posted: ‎2026-05-04 04:41 PM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-04 04:41 PM

JerryBenny18 online changes are made in the way you have described.  There is also a virtual connect mode where you can make changes (but only those that can be made online) to the project offline.  Reconnect as equal and then build online.  
In both cases however there are changes that require a rebuild all.  In this case you must stop the processor to undertake a full download.

Trial and error with the offline mode is the best way to detect which changes require a rebuild all.  In this case when a change is made open the PLC Build menu to see what options are available.  If only the "rebuild all" is available, then you must stop the PLC for a full download. 
In the virtual connect mode the build changes option should only be undertaken when online.  As soon as build or rebuild all is undertaken the projects are no longer equal.

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

ciupol
ciupol
Mentor

Posted: ‎2026-05-05 04:27 AM

1 Like
0
965
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-05 04:27 AM


@jerrybenny18 wrote:

 necessitates a PLC download even if it is only changing a few lines of logic? 


I exactly know what you mean. In Rockwell when  you made a small change the online change is almost instantaneous. In Control Expert it takes much longer and looks and feels like a download. But that just how it is in Schneider. Still the concept is the same but the execution is completely different.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore