Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-12 06:30 AM
Does anyone have a sample architecture for an M580 PLC using BMENOR2200H modules in a Hot Standby configuration?
Also, what is the recommended approach for connecting to a DNP3 Master when the BMENOR2200H is configured as a DNP3 Slave?
Can data from the NOR module be transmitted to a DNP3 Master through a BMENOC module, or is a direct physical connection to the NOR module mandatory for DNP3 communication?
Any sample network architecture or implementation guidance would be greatly Appreciated.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-13 03:14 PM
Hi @jouharn,
There is one TVDA, “How Can I Build an Integrated Telemetry and Remote SCADA System?”, which covered the BMENOR2200H module in the M580 HSBY configuration setup.
Check the link below for more details:
How Can I Build an Integrated Telemetry and Remote SCADA System?
In this TVDA, the BMENOR modules are configured as the DNP3 Server and communicate with the DNP3 (Client) Master station SCADA.
The sample architecture used in this TVDA is attached for your reference.
The BMENOR module Ethernet connection can be made either through the Control Ports (ETH1/ETH2) on the front of the BMENOR2200H or through an enabled backplane port. The backplane port is permanently connected to the M580 Ethernet backplane.
NOTE: When the BMENOR module is configured as a DNP3 or IEC 60870-5-104 (IEC 104) server and is used in an M580 High Availability (HSBY) architecture, the two BMENOR modules, one installed in the primary rack and the other in the standby rack, must be able to communicate with each other to synchronize events between themselves. The customer could choose which way the events could be synchronized, either using the backplane port or using the control ports, as shown in the figure below.
In the TVDA architecture, the front Ethernet control ports are used for synchronization of the events between two modules and for the DNP3 Master Station connectivity.
As you can see from the above explanation, there are multiple ways to access the BMENOR module; the best way depends on the customer requirement, current network design, and the desired level of network segmentation, security, and maintainability.
If you provide the exact customer requirement and the current network design then I can help you point out the best way to connect the BMENOR module but with the limited information that you shared In my opinion, you should use the BMENOR module front control port for the DNP3 connectivity, which provides the proper isolation between the networks, and make sure both modules are connected through the network for event synchronization and the Master station communication.
NOTE: The two front Control ports, as of now, do not support redundancy protocols (RSTP) that will be available in the future, so proper network design consideration is needed to avoid any storms or loops in the network.
I suggest you check the BMENOR module user guide to get more detailed information about the connectivity from the link below.
https://www.se.com/il/en/download/document/PHA90072/.
I hope the above explanation provides help. If you need further information or explanation, let me know or contact me through Teams.
Best Regards,
Wasif
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-15 07:33 AM . Last Modified: 2026-08-15 07:43 AM
Thanks @Siddiqui for the detailed explanation and for sharing the TVDA architecture reference.
I understand the concept of using the BMENOR control ports for DNP3 Master /SCADA communication. However, my main concern is regarding the redundant communication design, particularly in scenarios where the communication paths need to use different IP subnets.
The objective is to provide redundant communication paths while maintaining network separation through different subnets.
My uncertainty is around the solution where the NOC modules are used for the upstream network connections, while the BMENOR communicates via its backplane port through the NOC modules.
Thank you for your guidance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-17 03:01 AM
Hi @jouharn ,
Thank you for your response and for clarifying the requirement.
To meet your requirement, check my comments below:
As I explained previously, the BMENOR backplane port is always connected to the M580 Ethernet backplane, and there is no way to disable this connectivity.
So now you have two paths to access a BMENOR module; both of them are in different networks. The BMENOC0321 IP forwarding provides logical isolation between the upstream SCADA connectivity and the M580 Ethernet backplane port.
FYI, when the BMENOR modules launched it came with the backplane port only; there were no control ports, and during that time the BMENOR module could be accessed in many ways, as I explained in my previous comments in a flat network. One way is to utilize the BMENOC0321 with IP forwarding enabled to access the NOR module through its backplane port.
NOTE:
Besides that, if you could share more details in terms of the overall network design and how many M580 HSBY sets with the NOR modules are in the network architecture, that will clarify the design basis.
I hope the above comments will provide help.