M580 P580320 in timer events programm timer0 will not executed.
%S38 is MAST Task 1
%SW140=100 ms
Seconds issue .
io events also dont working.
in module BMX EHC0200 Channel O is presset to evt0.
Please tell me how i need configure my project.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-07-09 11:26 PM
Provide a copy of the project to this chat (.zef and .STU version) and we can have a quick look. Otherwise you may need to talk to your local support team.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-08-31 08:28 AM
Hi Trinxs1,
i have a issue with io-evente solved.
For all if intersting:
1. In HW-Config activate event --> evt 0 event=enable
for positive edge of IN_CAPT
2. x.EVT_CAPT_1_ENABLE=true
3. x.VALID_CAPT_1=true
4. x. FORCE_ENABLE=true
5. x.FORCE_REF trig by start to 1
create your programm in events/I/O Events/evt0.
Enjoy !