Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

IO Scanning - Modbus Function Code-23 Exception Error

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Re: IO Scanning - Modbus Function Code-23 Exception Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
jouharn
jouharn Contributor
Contributor

Posted: ‎2024-05-29 05:03 AM

0 Likes
4
3358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-29 05:03 AM

IO Scanning - Modbus Function Code-23 Exception Error

I am getting an error message in Wireshark when i was trouble shooting a communication issue. It is noticed that PLC is sending function code-23 data request and not accepted by Slave device. 

Function Code-23 request is not sending frequently. it is occurring very rarely.  is there a way to control the function codes in IO Scanning or to avoid this exception messages?

Attachments
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 05. Networking & Communication
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MatthewM
MatthewM
Mentor

Posted: ‎2024-05-29 09:00 PM . Last Modified: ‎2024-05-30 08:54 PM

3 Likes
3
3323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-29 09:00 PM . Last Modified: ‎2024-05-30 08:54 PM

When you say it is rarely using FC 23, is it mainly using FC 03 and FC 16, and then occasionally probing with FC 23 to see if it works?

 

Some devices (M221 for example), you only need one line, and it tests FC 23 first, and if rejected, it breaks it up into a FC 03 and FC 16 automatically.  Perhaps the M580 is doing the same too.

 

If you want to make it robust and not have FC 23, make one I/O scanning line for the read and one for the write (one 0 write size and the other 0 read size).  This will make it use FC03 and FC16 and you shouldn't see any FC 23.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

SEStig
SEStig Contributor
Contributor

Posted: ‎2024-09-05 07:11 PM

In response to MatthewM
0 Likes
1
3087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 07:11 PM

This is the way.....

 

The M580 does use FC23 in preference to a separate read and write if it can in one line. Splitting into two lines stops this but consumes more resources. If the FC23 is rejected it will then revert to 3 and 16.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

jouharn
jouharn Contributor
Contributor

Posted: ‎2024-09-05 09:45 PM

In response to SEStig
0 Likes
0
3068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 09:45 PM

Thanks for your reply 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
MatthewM
MatthewM
Mentor

Posted: ‎2024-05-29 09:00 PM . Last Modified: ‎2024-05-30 08:54 PM

3 Likes
3
3323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-29 09:00 PM . Last Modified: ‎2024-05-30 08:54 PM

When you say it is rarely using FC 23, is it mainly using FC 03 and FC 16, and then occasionally probing with FC 23 to see if it works?

 

Some devices (M221 for example), you only need one line, and it tests FC 23 first, and if rejected, it breaks it up into a FC 03 and FC 16 automatically.  Perhaps the M580 is doing the same too.

 

If you want to make it robust and not have FC 23, make one I/O scanning line for the read and one for the write (one 0 write size and the other 0 read size).  This will make it use FC03 and FC16 and you shouldn't see any FC 23.

Reply

Link copied. Please paste this link to share this article on your social media post.

SEStig
SEStig Contributor
Contributor

Posted: ‎2024-09-05 07:11 PM

In response to MatthewM
0 Likes
1
3087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 07:11 PM

This is the way.....

 

The M580 does use FC23 in preference to a separate read and write if it can in one line. Splitting into two lines stops this but consumes more resources. If the FC23 is rejected it will then revert to 3 and 16.

Reply

Link copied. Please paste this link to share this article on your social media post.

jouharn
jouharn Contributor
Contributor

Posted: ‎2024-09-05 09:45 PM

In response to SEStig
0 Likes
0
3068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 09:45 PM

Thanks for your reply 

Reply

Link copied. Please paste this link to share this article on your social media post.

jouharn
jouharn Contributor
Contributor

Posted: ‎2024-09-05 09:45 PM

In response to MatthewM
0 Likes
0
3068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 09:45 PM

Thank you 😊 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore