How to disable user login when using webserver

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Kers
Crewman
Crewman

How to disable user login when using webserver

Hello everyone,

 

The question is simple. I designed a webserver and when a type in the web this: 192.168.100.10:8080/index.htm to see the webserver I am asked for a user and a password in order to see the webserver. I know the user and the password but I want to disable this. I want to see the webserver without having to log in. I am using Machine Expert for the programming of the M241.

 

Can anyone tell me how to disable this? I've tried a couple of tricks but none worked.

 

Thanks in advance!

 

Kind regards!

Tags (1)
1 Reply 1
SteveAndjic
Ensign Ensign
Ensign
0 Likes
0
133

Re: How to disable user login when using webserver

Hi 

 

You need to log into the main webserver of the PLC (192.168.10.100 only) in your case

 

go to maintenance tab

click on user user management and disable user accounts management

 

Regards

 

Steve

 
 

disable user management.jpg

Tags (1)