Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to detect Modbus Communication Failure at Modicon M580?

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Re: How to detect Modbus Communication Failure at Modicon M580?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
9
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
RuchirSomani
RuchirSomani
Explorer

Posted: ‎2025-05-19 04:43 AM

0 Likes
14
13762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 04:43 AM

How to detect Modbus Communication Failure at Modicon M580?

Hi,

 

I need to understand how to find/configured in Control Expert for M580 whether Modbus Communication with any Modbus Slave device is working or has stopped ?
Is there any fail/error bit/code to sense this ?

 

Right now as values gets transferred between M580 and PSO over Modbus TCP,  the value gets stuck in PSO if downstream devices stop communication with M580 for any reason.
Is it also possible to convert this value automatically to "ZERO" in case the Modbus communication with field device breaks.

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hennie_Smith
Hennie_Smith Mentor
Mentor

Posted: ‎2025-05-19 08:50 PM

0 Likes
2
13737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 08:50 PM

Good day,

 

1. Yes you can monitor the Freshness bit in the Device DDT variable which is created when adding modbus device.

 

Hennie_Smith_1-1747712812166.png

 

Secondly to set the values to 0 if comms fail, open the NOC/CPU in the DTM browser and go to the Request settings of the modbus device. Each request can be set to 'Set to Zero' under the Last Value column. 

 

Hennie_Smith_2-1747712909481.png

 

Regards,

Hennie Smith

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

YONGHO-KIM
YONGHO-KIM Mentor
Mentor

Posted: ‎2025-05-19 10:05 PM

0 Likes
0
13726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 10:05 PM

1. I have implemented communication fault/normal status detection using the 'Gest' value from Read_Var.
The second word of the GEST value is 0 when communication is normal, and any value greater than 0 indicates an error.
Please refer to the attached PDF file for more details, and feel free to contact us if you have any questions.

YONGHOKIM_0-1747717446500.pngYONGHOKIM_1-1747717475692.png

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

YONGHO-KIM
YONGHO-KIM Mentor
Mentor

Posted: ‎2025-06-18 08:31 PM

In response to RuchirSomani
0 Likes
0
13440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 08:31 PM

1. The file I attached was applied to the BMXNOM card. Therefore, the same configuration can be applied to the NOM card as well.
2. Does the freezing issue occur when communication is lost with the device connected to the BMXNOM0200?
If so, please refer to the following link for more information:
https://community.se.com/t5/Modicon-PAC-Forum/BMXNOM0200-READ-VAR/m-p/487416#M1274
3. If the issue is not related to point 2, please increase the polling interval at the READ_VAR EN input as shown in the attached image.
4. Compare the GEST values between normal and abnormal communication cases.
5. If you have any further questions, feel free to reply.image.png

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
Hennie_Smith
Hennie_Smith Mentor
Mentor

Posted: ‎2025-05-19 08:50 PM

0 Likes
2
13738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 08:50 PM

Good day,

 

1. Yes you can monitor the Freshness bit in the Device DDT variable which is created when adding modbus device.

 

Hennie_Smith_1-1747712812166.png

 

Secondly to set the values to 0 if comms fail, open the NOC/CPU in the DTM browser and go to the Request settings of the modbus device. Each request can be set to 'Set to Zero' under the Last Value column. 

 

Hennie_Smith_2-1747712909481.png

 

Regards,

Hennie Smith

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

YONGHO-KIM
YONGHO-KIM Mentor
Mentor

Posted: ‎2025-05-19 10:05 PM

0 Likes
0
13727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-19 10:05 PM

1. I have implemented communication fault/normal status detection using the 'Gest' value from Read_Var.
The second word of the GEST value is 0 when communication is normal, and any value greater than 0 indicates an error.
Please refer to the attached PDF file for more details, and feel free to contact us if you have any questions.

YONGHOKIM_0-1747717446500.pngYONGHOKIM_1-1747717475692.png

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

RuchirSomani
RuchirSomani
Explorer

Posted: ‎2025-06-18 01:18 AM

In response to Hennie_Smith
0 Likes
1
13460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 01:18 AM

Hi,
Thanks a lot for your reply.

1) For what you have shared with NOC card, is same feature available with NOM card as well as we are polling around 10 Nos. of Modbus Serial devices using NOM card in M580.

2) Also, we have observed randomly data of MFM(Multi Function Energy meter)getting stuck while using READ VAR block to poll MFM(Multi Function Energy meter) for 10 Nos. MFMs in one single loop.

What is further way to diagnose such issues  i.e. how to understand if query length is too high or if we need to increase delay period between 2 polls of Modbus - this is for Modbus Serial(RTU) communication only. Does M580 inherently supports protocol tracing ?

Looking forward to your support.

Thanks & Regards

Ruchir Somani

Reply

Link copied. Please paste this link to share this article on your social media post.

ag56
ag56
Explorer

Posted: ‎2025-06-18 01:20 PM

1 Like
7
13438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 01:20 PM

Hello Ruchir,

 

There are some key concepts to take into account when implementing READ_VAR function.

 

First, you must specify the timeout period in the third register of the GEST array. A value of 5 means 500 ms and should normally be enough.

Please note that the NOM is configured with its own default answer delay (10 * 100 = 1000ms) and 3 retries. The timeout set in the third register should be greater than the answer delay time X number of retries.

You can reduce the default answer delay and set the number of retries to 0 to speed out the process if needed.

 

Second, it is recommended to expose the READ_VAR EN-ENO pins, then negate the EN pin and connect bit 0 (Active) of the first GEST register to it. This will disable the block call when a communication session is active.

 

Third, for serial communication avoid using more than one READ_VAR in parallel for the same NOM channel. If you are polling several devices on the same line, you need to manage the order in which they are called. For this purpose I am attaching a DFB based on DATA_EXCH function which is designed to manage as many devices as required sequentially and cyclically by proper parametrization. This all-in-one solution DFB requires no extra code. However, I do not have it documented in English so you will probably need some help to implement it. If you are interested in testing it, I can provide some simple examples.

Best Regards.

Attachments
EXCH_MULTI_N.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

YONGHO-KIM
YONGHO-KIM Mentor
Mentor

Posted: ‎2025-06-18 08:31 PM

In response to RuchirSomani
0 Likes
0
13441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 08:31 PM

1. The file I attached was applied to the BMXNOM card. Therefore, the same configuration can be applied to the NOM card as well.
2. Does the freezing issue occur when communication is lost with the device connected to the BMXNOM0200?
If so, please refer to the following link for more information:
https://community.se.com/t5/Modicon-PAC-Forum/BMXNOM0200-READ-VAR/m-p/487416#M1274
3. If the issue is not related to point 2, please increase the polling interval at the READ_VAR EN input as shown in the attached image.
4. Compare the GEST values between normal and abnormal communication cases.
5. If you have any further questions, feel free to reply.image.png

Reply

Link copied. Please paste this link to share this article on your social media post.

RuchirSomani
RuchirSomani
Explorer

Posted: ‎2025-07-11 11:03 PM

In response to ag56
0 Likes
3
13165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-11 11:03 PM

Hello,

Thanks for your reply. We also feel that there is problem of proper sequencing as we are trying to poll in total 37 devices across 2 NOM cards.


We have also came across a scenario wherein we kept just one "READ_VAR" block for one particular channel i.e. one serial channel dedicated for 1 RS485 Modbus device and after loading the program it does not generate any Modbus Query (NO ORANGE LED INDICATION ON NOM CARD).
And as soon as we shift this entire "READ_VAR" logic to some different page of the logic section, it starts generating modbus query without any changes(just the change of page).

 

It shall be really helpful if you share some example how to carry out necessary time grading for each Modbus poll so as to avoid overlapping.

Meanwhile to get rid of RS485 polling issues, we also tried using Modbus Serial to TCP converter in between and then carry out polling using NOC Card. But there as well, we faced strange challenge wherein as soon as we create 2nd request, the data goes haywire. Please find attached photo & video for your reference.

Request you to guide how we can resolve this issue for NOC card as well.

Attachments
Issue 2 Video.mp4
Issue 2 - Effects at SCADA.mp4
Reply

Link copied. Please paste this link to share this article on your social media post.

YONGHO-KIM
YONGHO-KIM Mentor
Mentor

Posted: ‎2025-07-16 07:44 PM

In response to RuchirSomani
0 Likes
2
13158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-16 07:44 PM

  1. The number of Modbus TCP devices that the BMENOC module can support is as follows:

    • Please check whether the number of devices exceeds the supported limit.
    • If you could upload the project file, we will review the configuration settings for you.
    • YONGHOKIM_0-1752720264095.png

       

  2. Regarding the BMXNOM module, please refer to the information I previously provided.

    • Again, if you upload the project file, we will check the configuration settings for this part as well.
Reply

Link copied. Please paste this link to share this article on your social media post.

RuchirSomani
RuchirSomani
Explorer

Posted: ‎2025-07-16 10:17 PM

In response to YONGHO-KIM
0 Likes
1
13141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-16 10:17 PM

Hello,
Thanks a lot for your reply. Please find our response.
1. We are trying to get data from only 1 No. TCP Server installed(as Modbus Serial to TCP Gateway Device) for which we shall at maximum create 13 Nos. of request with each request polling 96 nos. of 16-bit registers.

 

2. We have gone through your suggestion for BMXNOM card as earlier shared, but things are not yet particularly clear how we implement proper polling pattern for total 38 Nos. of Modbus Serial devices directly on 2 Nos. of NOM cards.
Please find attached our configuration for your further review where we have configured RS485 based serial polling for 38 Nos. of devices across 2 Nos. of NOM cards.

Attachments
UB_PLC_READ_VAR_SERIAL (MFM_TO_NOM_TO_PSO.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

MARTIN_NEILL
MARTIN_NEILL
Explorer

Posted: ‎2025-07-19 11:17 PM

In response to ag56
0 Likes
0
13053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-19 11:17 PM

could you please forward any documentation regarding your dbf. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

YONGHO-KIM
YONGHO-KIM Mentor
Mentor

Posted: ‎2025-07-20 07:35 PM

In response to RuchirSomani
0 Likes
0
13064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-20 07:35 PM

YONGHOKIM_0-1753065164771.png

The 'Modbus_TCP_Test' FBD has been created.
The READ_VAR block has been configured for Modbus TCP communication.
Please proceed with testing the setup.

Attachments
BACKUP_250721.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BBB1
BBB1
Explorer

Posted: ‎2025-09-26 08:18 AM

0 Likes
0
11229
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-26 08:18 AM

Subject: READ_VAR / WRITE_VAR not exchanging data with Modbus TCP device (no GEST errors)

Hello everyone,

I’m having an issue with Modbus TCP communication between my M580 PLC and a current rectifier for electrolysis (EWC device) using READ_VAR and WRITE_VAR blocks in EcoStruxure Control Expert v15.

Both blocks execute without any errors – GEST[3] = 0 for READ_VAR, and WRITE_VAR shows some data exchange activity – but no actual data is being read or written.

I’ve already tried several address formats in the ADDM string:

  • '0.2.0{172.169.101.2}' → works (no errors, but no data)
  • '0.2.0{172.169.101.2}1' → doesn’t work
  • '0.2.0{172.169.101.2}TCP.MBS' → gives Error 3 (incorrect address format)

The device responds correctly when tested with ModScan and KEPServerEX.

Could someone please advise what might cause READ_VAR and WRITE_VAR to show no communication errors but still not exchange data?
Any working example or clarification on proper addressing for Modbus TCP would be very helpful.

Thank you in advance for your time and support.

Best regards

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

AV_ARUN
AV_ARUN Explorer
Explorer

Posted: ‎2025-11-06 10:43 PM

In response to ag56
0 Likes
0
8851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 10:43 PM

Hi Can you share some example backups. 

Reply

Link copied. Please paste this link to share this article on your social media post.

ciupol
ciupol
Mentor

Posted: ‎2025-11-10 05:36 AM

In response to ag56
0 Likes
0
8683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-10 05:36 AM


@ag56 wrote:

 

For this purpose I am attaching a DFB based on DATA_EXCH function which is designed to manage as many devices as required sequentially and cyclically by proper parametrization. This all-in-one solution DFB requires no extra code. However, I do not have it documented in English so you will probably need some help to implement it. If you are interested in testing it, I can provide some simple examples.

Best Regards.


Can you provide the documentation you have. We can probably use some online translator and get a good idea how to use your block.

Reply

Link copied. Please paste this link to share this article on your social media post.

PeiHsin
PeiHsin Explorer
Explorer

Posted: ‎2025-11-20 12:31 AM

0 Likes
0
8196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-20 12:31 AM

Is there any other way such as diagnostic log to detect if Modbus is disconnected before? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore