Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ERROR_INVALID_CREDENTIALS M580 HSBY Firmware update from 3.20 to 4.10

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • ERROR_INVALID_CREDENTIALS M580 HSBY Firmware update from 3.20 to 4.10
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
gretarmark_
gretarmark_
Contributor

Posted: ‎2023-06-18 11:00 AM

0 Likes
4
4334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-18 11:00 AM

ERROR_INVALID_CREDENTIALS M580 HSBY Firmware update from 3.20 to 4.10

Hi there,

I am trying to update the firmware in M580 BMEH2040 HSBY system (level 2 for R IO), from 3.20 to 4.1.

I am using usb connection and Automation Device Maintenance.

The update always stops at 100% when I'm going from version 3.20 to 3.99 and gives an error saying something like

    "ERROR_INVALID_CREDENTIALS"

 

I have tried to reset the M580 BMEH2040 units by following these guides:
https://community.se.com/t5/Modicon-PAC-Forum/How-to-Reset-a-M580-CPU/td-p/378726

 

but still it won't work. I use password fwdownload and nothing changes.

I also tried to deactivate the firewall on the virtual machine I am using, didn't work.

Hope you can help me.

Regards,
Grétar Már

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 05. Networking & Communication
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
gretarmark_
gretarmark_
Contributor

Posted: ‎2023-08-29 01:41 AM

1 Like
0
4029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-29 01:41 AM

Hi @Kurosaki and @Ricard 

What worked for me is that I used Unity Loader to upgrade to version 3.9 and after that I was able to use Automation Device Maintenance to upgrade from 3.9 to 4.1.

Best regards, 
Grétar

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Kurosaki
Kurosaki Explorer
Explorer

Posted: ‎2023-08-23 02:35 AM

0 Likes
0
4100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-23 02:35 AM

Hello Gretarmark_

I hope you already found a solution.

In case you are still facing this issue please use the following instruction provided by Schneider Electric:

Modicon M580 Controller Firmware (schneider-electric.com)

After the installation of FW 3.99 you have to follow the the instructions from Step 2 in the PDF.
The necessary credentials can be found on page 20.
Important is that you need to remove and add the device again as described on Page 19

Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Ricard Troubleshooter
Troubleshooter

Posted: ‎2023-08-28 02:22 AM

0 Likes
0
4053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-28 02:22 AM

Hello Grétar

 

After the update try to connect using the factory IP. I attached an example video.

 

How to Upgrade M580 CPU Legacy Firmware to Version 4.xx | Schneider Electric Support

https://www.youtube.com/watch?v=AWipD9PwKWg

 

On the other hand, you should check that you have the latest firmware and EADM versions. I have attached some additional links.

 

MODICON M580 BMEx58x0x0 intermediate Firmware OS3.99.07

https://www.se.com/ww/en/download/document/BMEx58x0x0_SV03.99.07/

 

Modicon M580 BMEx58x0x0 Firmware SV04.10.13

https://www.se.com/ww/en/download/document/BMEx58x0x0_SV04.10/

 

EcoStruxure Automation Device Maintenance (EN) Version : V3.2.124

https://www.se.com/ww/en/download/document/EADM/

 

If you still can't update the CPU, contact the Schneider technical support in your country

 

Good Luck!

Ricard

Reply

Link copied. Please paste this link to share this article on your social media post.

gretarmark_
gretarmark_
Contributor

Posted: ‎2023-08-29 01:41 AM

1 Like
0
4029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-29 01:41 AM

Hi @Kurosaki and @Ricard 

What worked for me is that I used Unity Loader to upgrade to version 3.9 and after that I was able to use Automation Device Maintenance to upgrade from 3.9 to 4.1.

Best regards, 
Grétar

 
Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Ricard Troubleshooter
Troubleshooter

Posted: ‎2023-09-19 11:27 PM

0 Likes
0
3946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-19 11:27 PM

Hello Grétar

 

After the update try to connect using the factory IP. I attached an example video.

 

How to Upgrade M580 CPU Legacy Firmware to Version 4.xx | Schneider Electric Support

https://www.youtube.com/watch?v=AWipD9PwKWg

 

On the other hand, you should check that you have the latest firmware and EADM versions. I have attached some additional links.

 

MODICON M580 BMEx58x0x0 intermediate Firmware OS3.99.07

https://www.se.com/ww/en/download/document/BMEx58x0x0_SV03.99.07/

 

Modicon M580 BMEx58x0x0 Firmware SV04.10.13

https://www.se.com/ww/en/download/document/BMEx58x0x0_SV04.10/

 

EcoStruxure Automation Device Maintenance (EN) Version : V3.2.124

https://www.se.com/ww/en/download/document/EADM/

 

If you still can't update the CPU, contact the Schneider technical support in your country

 

Good Luck!

Ricard

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore