Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
PowerLogic
PowerLogic ION8650 series
KimS
KimS Contributor
Contributor
Posted: ‎2026-03-25 09:43 AM
844
Is the ION8650 internally grounded for the vRef?
Customer wants to know if they have 2PTs and 2CTs to one meter in parallel he does not multiple grounds. Form 35S ION8650.
Are current terminals, I11, I12, I31, and I32, are they internally grounded
  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
View products (1)
  • ION8000
DanL
DanL Champion
Champion
Posted: ‎2026-03-27 08:58 AM
The "Vref" measurement terminal of the ION8650 is not ground bonded, but instead has a 5meg-ohm input impedance (to ground).
The current terminals, I11, I12, I31, and I32, are NOT internally grounded.
You should ensure the ION8650 itself is grounded; either via the AUX power supply, socket base, or ground screw on the bottom of the socket meter.
Charles_Murison
Champion
Posted: ‎2026-03-26 07:20 AM
If the system has PTs with a grounded secondary, you need to connect the secondary ground to Vref to be able to invert PT polarity.
If not using PTs, DO NOT connect Vref to ground, Connect Vref to Vb.
Charles
DanL
DanL Champion
Champion