Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84520members
353747posts

Where can i find the on/off voltage range of the digital input signal on the ION7650?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Jeon
Ensign
Ensign
0 Likes
2
265

Where can i find the on/off voltage range of the digital input signal on the ION7650?

hi all,

 

Where can i find the on/off voltage range of the digital input signal on the ION7650?

 

asd.png

Can you tell me the information about the range of on/off state for ion7650 as above?

 

thanks a lot.

 

Best regarlds

Tags (1)

Accepted Solutions
DanL
Commander Commander
Commander

Re: Where can i find the on/off voltage range of the digital input signal on the ION7650?

The ION7650 digital inputs have internal "self-excitation" and will register as "Closed" when an Sn (n=1 to 8 ) digital input is connected to Scom with a voltage between 0V (short) and 130VDC.

  • A wire with less than 10k Ohms (ideally less than 1 Ohm) across the terminals will register as CLOSED.
  • A connection with a (non-negative) voltage up to 130VDC applied (ideally less than 30VDC) will register as CLOSED.
  • A negative voltage exceeding -20V is applied (recommended practice is to provide an open circuit instead of a negative voltage) will register as OPEN.
  • A connection with more than 1Meg Ohms (ideally more than 10 Meg Ohm) across the terminals will register as OPEN.

See Answer In Context

Tags (1)
2 Replies 2
Charles_Murison
Picard Picard
Picard
0 Likes
1
244

Re: Where can i find the on/off voltage range of the digital input signal on the ION7650?

Hello @Jeon,

 

The screenshot you provided is likely from ION9000, PM800 or ION7400 meter. The ION7650 meters uses a completely different design. There are no ranges, there is open or there is close.

https://www.se.com/ww/en/download/document/70002-0247/, page 11. The digital inputs require Open/Close signal with or without external DC voltage.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
DanL
Commander Commander
Commander

Re: Where can i find the on/off voltage range of the digital input signal on the ION7650?

The ION7650 digital inputs have internal "self-excitation" and will register as "Closed" when an Sn (n=1 to 8 ) digital input is connected to Scom with a voltage between 0V (short) and 130VDC.

  • A wire with less than 10k Ohms (ideally less than 1 Ohm) across the terminals will register as CLOSED.
  • A connection with a (non-negative) voltage up to 130VDC applied (ideally less than 30VDC) will register as CLOSED.
  • A negative voltage exceeding -20V is applied (recommended practice is to provide an open circuit instead of a negative voltage) will register as OPEN.
  • A connection with more than 1Meg Ohms (ideally more than 10 Meg Ohm) across the terminals will register as OPEN.
Tags (1)