Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84749members
354179posts

What is the accuracy of PM8000 for demand readings?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Sepehr_Zarrabi
Lieutenant Lieutenant
Lieutenant
0 Likes
3
640

What is the accuracy of PM8000 for demand readings?

Looking for the accuracy of the following demand measurements in the PM8000:

 - Current demand

 - Active power demand

 - Reactive power demand

 - Apparent power demand

 

Thank you!

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
0
616

Re: What is the accuracy of PM8000 for demand readings?

The biggest issue with demand accuracy spec is that a test can span a huge dynamic range (signal variation during the interval). For steady state lab conditions and proper configuration, the demand accuracy should be the same as power accuracy.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
3 Replies 3
Charles_Murison
Picard Picard
Picard
0 Likes
1
635

Re: What is the accuracy of PM8000 for demand readings?

Hello @Sepehr_Zarrabi ,

 

I think I need a bit more of the context behind this question. Is there a standard you are trying to meet I do not know about? 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Sepehr_Zarrabi
Lieutenant Lieutenant
Lieutenant
0 Likes
0
631

Re: What is the accuracy of PM8000 for demand readings?

Hello Charles,

 

I don't think this is a spec-related question.  My BDS reached out to me with this question.  I believe the question came from a customer.  We can get in touch with her if you need more info.  Please reach out to me directly.

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
0
617

Re: What is the accuracy of PM8000 for demand readings?

The biggest issue with demand accuracy spec is that a test can span a huge dynamic range (signal variation during the interval). For steady state lab conditions and proper configuration, the demand accuracy should be the same as power accuracy.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)