Upload a partial framework *.FWN using ION Setup 3.0

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: Upload a partial framework *.FWN using ION Setup 3.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa92954
Crewman sesa92954 Crewman
Crewman

Posted: ‎2014-01-31 09:04 AM . Last Modified: ‎2020-04-22 01:52 AM

0 Likes
2
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-31 09:04 AM

Upload a partial framework *.FWN using ION Setup 3.0

Hello everybody!

 

I've created a function in Designer using the option "Copy to Framework". Now, I have a file with the extension *.FWN. Our customer doesn't have ION Enterprise so I need he can upload this *.FWN using ION Setup.

 

I've seen in ION Setup when I'm going to send a new template, there is the option to change the file extension that you'll send, at this point you can choose beetwen *.DCF and *.FWN.

After choose *FWN, I was trying to send the *FWN created previously but appears a compatibility error.

 

Could somebody help me?

Thanks in advance.

Labels
  • Labels:
  • ION Setup
Tags (3)
  • Tags:
  • framework
  • ion_setup
  • partial
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2014-01-31 09:12 AM

0 Likes
1
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-31 09:12 AM

Unfortunately ION Setup can only upload complete device framework files and not partial ones.  ION Designer allows users to specify how to handle overlapping of existing modules (either overwriting the existing modules or just appending the partial modules to available ones).  ION Setup does not have this capability and uses a process which speeds up downloading but at the cost of unable to maintain the existing template.

The only other thing I can suggest other than the customer getting ION Designer himself is for you to locate the same meter as the customer, paste his template onto that device and then use ION Designer yourselft to paste your partial framework (again needing to decide whether to overwrite or append the new modules).  Once completed, you could save the complete template as either a DCF or FWN file and send that complete file to the user who could use ION Setup to download to his meter.

Reply
sesa92954
Crewman sesa92954 Crewman
Crewman

Posted: ‎2014-01-31 09:33 AM

0 Likes
0
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-31 09:33 AM

The problem is that this procedure have to be carry out in 100 devices without clean its memory.

Please let me know if you know other ways to solve this trouble.

Thanks for your fast answer.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of