Hello everyone. I have two ION8650 meters "primary" and "secondary" connected to a GPS unit (which supports up to 32 devices). I configured both using ION Setup, but the "secondary" unit failed to synchronize. I have attached screenshots of both configurations.
You can see from the screenshots that the "secondary" unit is offset by 12 hours.
Any suggestions on how to fix this?
Link copied. Please paste this link to share this article on your social media post.
Hello @DanielMejia
Time since sync is for specific protocols like ION. It does not update when using other time sync options such as IRIG-B, or NTP.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @DanielMejia,
Chances are, IRIG-B is not able to adjust the clock of the meter by as much as is needed. I suggest changing to use ION protocol, then adjust the time of the meter then set back to IRIG-B.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi Charles. I tried your suggestion and it did sync, but the Time Since Sync/Reset keeps increasing and isn't updating. I've attached a photo of the last loaded configuration. Do you have any advice for this?
Link copied. Please paste this link to share this article on your social media post.
Hello @DanielMejia
Time since sync is for specific protocols like ION. It does not update when using other time sync options such as IRIG-B, or NTP.
Regards,
Charles