Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Technical Inquiry: HDPM6000 Application for Multi-Source Applications

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Technical Inquiry: HDPM6000 Application for Multi-Source Applications
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
AJPACHECO98
AJPACHECO98 Explorer
Explorer

Posted: β€Ž2026-08-04 07:22 AM

0 Likes
1
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2026-08-04 07:22 AM

Technical Inquiry: HDPM6000 Application for Multi-Source Applications

Hello team,

I have a question regarding the HDPM6000 application for multi-source lineups.

Currently, we are using the HDPM6000 Master Unit with an incoming meter (P/N: METSEHDPM6S480VC) as a special application in switchboards with a single incoming source and multiple feeders (METSEHDPM6S24WF.)

Attached/Below is a diagram of our standard setup for a single incoming source: we install a metering CT on the main incoming section, wire it to the HDPM head unit, and daisy-chain the CT strips in the feeder sections back to the main head unit.

AJPACHECO98_3-1785852881116.png

 

However, we are starting to receive requests for HDPM6000 applications in lineups with multiple incoming sources (e.g., Main-Main, Main-Generator, etc.).

Could you clarify the recommended approach for wiring the head unit in a multi-source configuration? I couldn't find specific documentation on this online.

My understanding is that a separate head unit would be required for each incoming source due to the single voltage reference limitation. If that is the case:

 

  1. Is a dedicated head unit required per incoming source? (Pic Bellow) 

  2. Can these head units be networked together via their Ethernet ports, two separate head/master units with displays, complete with individual sets of CTs and potential taps for each source?

  3. AJPACHECO98_2-1785852821664.png

  4. Or is it better to route the Generator signals through a CT strip module connected back to a single head unit?

AJPACHECO98_0-1785852449145.png

Thanks Team πŸ™‚ 

 

Attachments
Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: β€Ž2026-08-04 10:33 AM . Last Modified: β€Ž2026-08-04 10:55 AM

1 Like
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2026-08-04 10:33 AM

Hi @AJPACHECO98 

 

The proposed configuration featuring two separate HDPM6000 head units, each dedicated to an incoming source with its own voltage references and metering CTs, is the recommended architecture.

 

1. Multi-Source Applications

A separate HDPM6000 head unit is required for each independent power source (for example, Main-Main or Main-Generator systems).

Each head unit supports only one 3-phase voltage reference. Since power, energy, and power factor calculations rely on both current and voltage measurements, all CT strips connected to a head unit must be associated with the same source as that head unit's voltage reference.

 

Connecting feeders supplied by a different source to a head unit referenced to another source can result in inaccurate power and energy calculations, particularly when there are voltage differences, phase displacement, or when the sources are not synchronized.

Therefore, each incoming source should have:

  • Its own HDPM6000 head unit
  • Dedicated voltage reference connections
  • Associated incoming metering CTs
  • CT strips serving only the feeders supplied by that source

2. Ethernet Networking

Yes, multiple HDPM6000 head units can be connected via Ethernet, either by:

  • Daisy-chaining the head units using the built-in Ethernet ports, or
  • Connecting each head unit to a network switch

Each head unit operates as an independent metering system while allowing data aggregation through the network. Upstream systems such as PME, BMS, or other supervisory platforms can collect data from multiple HDPM6000 head units using supported Ethernet protocols.

 

Therefore, for a lineup with multiple incoming sources, use one HDPM6000 head unit per source. Connect the CT strips for each feeder group back to the corresponding head unit associated with that source, and network the head units together via Ethernet as required for centralized monitoring and visualization.

 

HMI Consideration:
Based on the provided diagram, the HMIs are connected to the HDPM6000 head units via RS-485. Therefore, the second Ethernet port (Eth1) remains available for standard Ethernet networking or daisy-chaining of HDPM6000 devices. The Ethernet HMI configuration restrictions described in the Installation Guide apply only when an HMI(only 10” HMI used in specific projects) is connected via Ethernet and do not apply to an RS-485-connected HMI.

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Reply 1
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: β€Ž2026-08-04 10:33 AM . Last Modified: β€Ž2026-08-04 10:55 AM

1 Like
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

β€Ž2026-08-04 10:33 AM

Hi @AJPACHECO98 

 

The proposed configuration featuring two separate HDPM6000 head units, each dedicated to an incoming source with its own voltage references and metering CTs, is the recommended architecture.

 

1. Multi-Source Applications

A separate HDPM6000 head unit is required for each independent power source (for example, Main-Main or Main-Generator systems).

Each head unit supports only one 3-phase voltage reference. Since power, energy, and power factor calculations rely on both current and voltage measurements, all CT strips connected to a head unit must be associated with the same source as that head unit's voltage reference.

 

Connecting feeders supplied by a different source to a head unit referenced to another source can result in inaccurate power and energy calculations, particularly when there are voltage differences, phase displacement, or when the sources are not synchronized.

Therefore, each incoming source should have:

  • Its own HDPM6000 head unit
  • Dedicated voltage reference connections
  • Associated incoming metering CTs
  • CT strips serving only the feeders supplied by that source

2. Ethernet Networking

Yes, multiple HDPM6000 head units can be connected via Ethernet, either by:

  • Daisy-chaining the head units using the built-in Ethernet ports, or
  • Connecting each head unit to a network switch

Each head unit operates as an independent metering system while allowing data aggregation through the network. Upstream systems such as PME, BMS, or other supervisory platforms can collect data from multiple HDPM6000 head units using supported Ethernet protocols.

 

Therefore, for a lineup with multiple incoming sources, use one HDPM6000 head unit per source. Connect the CT strips for each feeder group back to the corresponding head unit associated with that source, and network the head units together via Ethernet as required for centralized monitoring and visualization.

 

HMI Consideration:
Based on the provided diagram, the HMIs are connected to the HDPM6000 head units via RS-485. Therefore, the second Ethernet port (Eth1) remains available for standard Ethernet networking or daisy-chaining of HDPM6000 devices. The Ethernet HMI configuration restrictions described in the Installation Guide apply only when an HMI(only 10” HMI used in specific projects) is connected via Ethernet and do not apply to an RS-485-connected HMI.

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.