Does / Can ION7650 expose THD Ia, THD Ib, THD Ic, THD In and THD Vab, THD Vbc and THD Vca to Modbus registers?
Also, are the readings below (modbus registers from section PF/THD/Kfactor) taken in any observation period or are accumulated until manually reset?
Source #5 40266 V1 THD mx
Source #6 40267 V2 THD mx
Source #7 40268 V3 THD mx
Source #8 40269 I1 THD mx
Source #9 40270 I2 THD mx
Source #10 40271 I3 THD mx
if the THD mx represents max value on a observation period, what's the factory default for the observation period
if the THD mx represents accumulative max value is there a way to reset it without using ION setup or Vista?
Link copied. Please paste this link to share this article on your social media post.
Hi @madhav.sga
The default ION7650 Modbus map exposes only maximum THD values (THD mx) at registers 40266-40271 and does not provide instantaneous THD measurements. ION Meters Modbus Register Map.
Harmonic quantities such as voltage THD and current THD are available within the framework, Harmonics Module -> V1 Harmonics -> V1 Total HD, etc. and they can generally be exposed through custom Modbus mappings using Modbus Slave modules in ION Setup.
How to Map Custom Modbus Registers on the ION7650 Energy Meter
The THD mx registers represent peak-hold maximum values maintained by the framework's Min/Max modules. They are not based on a rolling observation window and remain stored until a reset occurs. Therefore, there is no factory-defined observation period associated with these registers.
Other than Master Reset using ION Setup, resetting the stored THD maximum values depends on the framework configuration. In many factory frameworks, a Min/Max reset can be performed by Master Reset from the meter front panel. Also By triggering External Pulse Module Harm MnMx Rset in ION Setup or Vista or Modbus write command to the 42010 Modbus register which is associated with the Harm MnMx Rset External Pulse Module.
Additional reset methods, such as Digital Inputs, may be implemented if configured within the framework. A change in the input state can generate an External Pulse(if Input Mode setup register is set to PULSE) that is linked to the Harm Min/Max module Reset input(via a Pulse Merge module with third external pulse), causing the stored THD maximum values to be cleared and restarted.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @madhav.sga
The default ION7650 Modbus map exposes only maximum THD values (THD mx) at registers 40266-40271 and does not provide instantaneous THD measurements. ION Meters Modbus Register Map.
Harmonic quantities such as voltage THD and current THD are available within the framework, Harmonics Module -> V1 Harmonics -> V1 Total HD, etc. and they can generally be exposed through custom Modbus mappings using Modbus Slave modules in ION Setup.
How to Map Custom Modbus Registers on the ION7650 Energy Meter
The THD mx registers represent peak-hold maximum values maintained by the framework's Min/Max modules. They are not based on a rolling observation window and remain stored until a reset occurs. Therefore, there is no factory-defined observation period associated with these registers.
Other than Master Reset using ION Setup, resetting the stored THD maximum values depends on the framework configuration. In many factory frameworks, a Min/Max reset can be performed by Master Reset from the meter front panel. Also By triggering External Pulse Module Harm MnMx Rset in ION Setup or Vista or Modbus write command to the 42010 Modbus register which is associated with the Harm MnMx Rset External Pulse Module.
Additional reset methods, such as Digital Inputs, may be implemented if configured within the framework. A change in the input state can generate an External Pulse(if Input Mode setup register is set to PULSE) that is linked to the Harm Min/Max module Reset input(via a Pulse Merge module with third external pulse), causing the stored THD maximum values to be cleared and restarted.
Best Regards,
-Mehran
L3 Expert Advanced metering