Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

THD Readings for ION7650

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • THD Readings for ION7650
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
madhav.sga
madhav.sga
Explorer

Posted: ‎2026-08-13 06:30 PM

0 Likes
1
318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-13 06:30 PM

THD Readings for ION7650

Does / Can ION7650 expose THD Ia, THD Ib, THD Ic, THD In and THD Vab, THD Vbc and THD Vca to Modbus registers?

 

Also, are the readings below (modbus registers from section PF/THD/Kfactor) taken in any observation period or are accumulated until manually reset? 

 

Source #5 40266 V1 THD mx
Source #6 40267 V2 THD mx
Source #7 40268 V3 THD mx
Source #8 40269 I1 THD mx
Source #9 40270 I2 THD mx
Source #10 40271 I3 THD mx


if the THD mx represents max value on a observation period, what's the factory default for the observation period

if the THD mx represents accumulative max value is there a way to reset it without using ION setup or Vista?


Labels
  • Labels:
  • ION7000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-14 11:03 AM . Last Modified: ‎2026-08-14 04:26 PM

1 Like
0
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-14 11:03 AM

Hi @madhav.sga 


The default ION7650 Modbus map exposes only maximum THD values (THD mx) at registers 40266-40271 and does not provide instantaneous THD measurements. ION Meters Modbus Register Map.

Harmonic quantities such as voltage THD and current THD are available within the framework, Harmonics Module -> V1 Harmonics -> V1 Total HD, etc. and they can generally be exposed through custom Modbus mappings using Modbus Slave modules in ION Setup.
How to Map Custom Modbus Registers on the ION7650 Energy Meter

The THD mx registers represent peak-hold maximum values maintained by the framework's Min/Max modules. They are not based on a rolling observation window and remain stored until a reset occurs. Therefore, there is no factory-defined observation period associated with these registers.

 

Other than Master Reset using ION Setup, resetting the stored THD maximum values depends on the framework configuration. In many factory frameworks, a Min/Max reset can be performed by Master Reset from the meter front panel. Also By triggering External Pulse Module Harm MnMx Rset in ION Setup or Vista or Modbus write command to the 42010 Modbus register which is associated with the Harm MnMx Rset External Pulse Module.

Mehran_Mehrnia_0-1786730625988.png

 

Additional reset methods, such as Digital Inputs, may be implemented if configured within the framework. A change in the input state can generate an External Pulse(if Input Mode setup register is set to PULSE) that is linked to the Harm Min/Max module Reset input(via a Pulse Merge module with third external pulse), causing the stored THD maximum values to be cleared and restarted.

 

Mehran_Mehrnia_0-1786749312545.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Reply 1
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-14 11:03 AM . Last Modified: ‎2026-08-14 04:26 PM

1 Like
0
310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-14 11:03 AM

Hi @madhav.sga 


The default ION7650 Modbus map exposes only maximum THD values (THD mx) at registers 40266-40271 and does not provide instantaneous THD measurements. ION Meters Modbus Register Map.

Harmonic quantities such as voltage THD and current THD are available within the framework, Harmonics Module -> V1 Harmonics -> V1 Total HD, etc. and they can generally be exposed through custom Modbus mappings using Modbus Slave modules in ION Setup.
How to Map Custom Modbus Registers on the ION7650 Energy Meter

The THD mx registers represent peak-hold maximum values maintained by the framework's Min/Max modules. They are not based on a rolling observation window and remain stored until a reset occurs. Therefore, there is no factory-defined observation period associated with these registers.

 

Other than Master Reset using ION Setup, resetting the stored THD maximum values depends on the framework configuration. In many factory frameworks, a Min/Max reset can be performed by Master Reset from the meter front panel. Also By triggering External Pulse Module Harm MnMx Rset in ION Setup or Vista or Modbus write command to the 42010 Modbus register which is associated with the Harm MnMx Rset External Pulse Module.

Mehran_Mehrnia_0-1786730625988.png

 

Additional reset methods, such as Digital Inputs, may be implemented if configured within the framework. A change in the input state can generate an External Pulse(if Input Mode setup register is set to PULSE) that is linked to the Harm Min/Max module Reset input(via a Pulse Merge module with third external pulse), causing the stored THD maximum values to be cleared and restarted.

 

Mehran_Mehrnia_0-1786749312545.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore