TCP Number of Connections PM8000, PM5000 and PM800 series

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
sesa82206
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
6
648

TCP Number of Connections PM8000, PM5000 and PM800 series

Team,

What is the max number of simultaneous TCP connections a:

-  PM8xxx can support?

- PM5xxx ?

- PM8xx ?

Regards,


Accepted Solutions
ram_kaushik
Admiral Admiral
Admiral
0 Likes
3
528

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

Ivan - from the PM8000 specification - 32 concurrent TCP/IP connections. Still looking into PM5000 since it is not captured in the spec..

See Answer In Context

6 Replies 6
ram_kaushik
Admiral Admiral
Admiral
0 Likes
3
529

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

Ivan - from the PM8000 specification - 32 concurrent TCP/IP connections. Still looking into PM5000 since it is not captured in the spec..

sesa56307_bridg
Lieutenant JG Lieutenant JG
Lieutenant JG

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

To be more specific, the 32 concurrent TCP/IP connections are dedicated to Modbus TCP (port 502), but a number of additional connections are also supported.

Here is a screenshot of a good summary from the PM8000 user manual:

7224

Usha
Lieutenant JG Lieutenant JG
Lieutenant JG

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

For PM5300 class of meters have been tested to support up to 3 concurrent TCP connections.

For PM5500 class of meter support up to 32 concurrent TCP connections.

Usha M R
JamesAZZO
Sisko | EcoXpert Master Sisko | EcoXpert Master
Sisko | EcoXpert Master
0 Likes
1
528

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

What is the difference between Modbus TCP and Modbus TCP (dedicated)?

sesa82206
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
528

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

Thank you Usha,

Are there any documents available tgat contain this onformation that I can share with customer? Specs doc, design guides, etc?

sesa64419
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: TCP Number of Connections PM8000, PM5000 and PM800 series

The PM8000 has 8 Ethernet connections that can be shared (used by) either ION, DNP or Modbus TCP or combination of all three.

There are also 32 Ethernet connections that can only be used by Modbus TCP.

So there are 32 dedicated (can only be used by) Modbus TCP connections, and there are up to 8 additional connections which could use Modbus TCP if desired (and you didn't want any ION or DNP connections).

I've heard some people call the 8 shared connections  "generic" connections as they can be used for either of the three protocols.

Modbus TCP is the only protocol that has both dedicated and shared connections, so they are differentiated in the table. The other protocols have dedicated connections (like IEC 61850).

Hope this helps.

Alana