Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Simulating sag, brownout, etc.. in the lab - How?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Simulating sag, brownout, etc.. in the lab - How?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
ron_kent
ron_kent
Explorer

Posted: ‎2026-10-26 10:17 AM

0 Likes
5
277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-26 10:17 AM

Simulating sag, brownout, etc.. in the lab - How?

We have a few PM8240 and ION9000 meters which are fantastic. We need to do some testing in our lab of simulating various power conditions like sag, brownout, etc.. with these meters. Is there a standard recommendation for this, or an inexpensive way outside of a full-size grid simulator that can do this? 

Labels
  • Labels:
  • ION9000
  • PM8000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-10-27 09:32 AM

1 Like
0
267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-27 09:32 AM

Hello @ron_kent ,

 

A lot depends on what kinds of tests you need to perform. For example if you need precise timing with specific voltage measurements compared to general meter behavior. If precise timing is required or very specific voltage measurements you would like need to look into equipment to give you those signals. If however you are looking for general meter behavior you could possibly look at using devices like a variac (variable autotransformer). 

 

Anything used will need to be electrically safe and in compliance with local electrical codes.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 5
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-10-27 08:25 AM

0 Likes
0
268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-27 08:25 AM

Hi @ron_kent 

 

The preferred method is to use a secondary-injection test set or programmable AC source to apply actual voltage signals to the meter. For example, if the Sag/Swell thresholds are configured at 90% and 110% of nominal voltage, the applied voltage can be reduced below 90% to simulate a sag or increased above 110% to simulate a swell.

 

Another possible method for demonstration purposes is to use the meter's Demo mode (Volts Mode as DEMO) and adjust the Nominal Voltage or PT ratio so that the simulated voltage falls outside the configured Sag/Swell thresholds.
However, this method is not recommended for validating actual meter behavior because not all meter modules and functions operate in Demo mode as they do with real voltage/current inputs.

 

Therefore, for meaningful laboratory testing of the PM8240 or ION9000, applying real signals using a secondary-injection test set, such as an OMICRON CMC or equivalent programmable source, would be the preferred approach.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-10-27 09:32 AM

1 Like
0
267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-27 09:32 AM

Hello @ron_kent ,

 

A lot depends on what kinds of tests you need to perform. For example if you need precise timing with specific voltage measurements compared to general meter behavior. If precise timing is required or very specific voltage measurements you would like need to look into equipment to give you those signals. If however you are looking for general meter behavior you could possibly look at using devices like a variac (variable autotransformer). 

 

Anything used will need to be electrically safe and in compliance with local electrical codes.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
CEFISE
CEFISE
Explorer

Posted: ‎2026-10-28 10:09 AM

1 Like
0
242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-10-28 10:09 AM

Hello Ron,

Event recording tests (sags/swells) can be conducted in a laboratory setting using Omicron test equipment that includes power quality (PQ) testing functionality.

As an additional recommendation, I suggest you consult the IEC 62586 standard, which establishes the requirements for power quality testing.

 

CEFISE_0-1793207324065.png

 

Best regards,
Gerardo Robledo

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2026-11-04 07:56 AM

0 Likes
1
163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-11-04 07:56 AM

Hello @ron_kent ,

Did you still need any help on this topic?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
ron_kent
ron_kent
Explorer

Posted: ‎2026-11-04 08:41 PM

0 Likes
0
148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-11-04 08:41 PM

These were all super helpful responses! I've been using the meters demo mode but didn't realize that there were some adjustable parameters. The Schneider team really thought of everything with these devices. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore