Retrieving data from ION7650 power analyser in ms time frame

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
NasseemIbrahim
Cadet

Retrieving data from ION7650 power analyser in ms time frame

Dear Support,

could you please advise if it is possible to retrieve the data from ION7650 in ms time frame.

Thanks

 


Accepted Solutions
DanL
Commander Commander
Commander

Re: Retrieving data from ION7650 power analyser in ms time frame

Yes, voltage and current can be configured to be recorded for short durations (based on event criteria) and then later retrieved using ION over the communications links.

Depending on your application requirements, you may choose to:

1. record instantaneous voltage and current in a Waveform Recorder
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=WaveformRecorderModule-045...

 

2. record one-cycle RMS every half-cycle in a Data Recorder (using a set of other helper modules to control trigger and enable logic)

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=DataRecorderModule-21B4C52...

See Answer In Context

Tags (1)
4 Replies 4
Charles_Murison
Picard Picard
Picard
0 Likes
3
335

Re: Retrieving data from ION7650 power analyser in ms time frame

Hello @NasseemIbrahim ,

 

This is a very loaded question, if you are asking if possible to get ms timestamps for the meter this could be possible, certain events are recorded with ms data for example sag/swell start and end times. The sag/swell log is triggered with disturbance end that has ms data.  

 

If you are asking about module update rates, different modules have different update speeds. Most modules will update every second, some modules update every half cycle. 

 

If you are asking about logging in the sub second rage, this gets tricky. While may be possible under certain conditions, do not recommend continuously logging at sub second intervals as there is a high chance of Flash ware.

 

If you are asking about response time this is even more loaded. The meter itself is a meter first with comms being a secondary task. If meter gets busy, may not respond to comms as fast as if meter is not busy. We cannot give a guaranteed response time.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
NasseemIbrahim
Cadet
0 Likes
2
310

Re: Retrieving data from ION7650 power analyser in ms time frame

Dear @Charles_Murison 

 

Many thanks for your below mail.

 

My question is related to the measured data like current and voltage. could I configure the ION7650 to record these value in ms time frame. and then I can export this reading.

 

Many thanks for your support

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
0
306

Re: Retrieving data from ION7650 power analyser in ms time frame

Hello @NasseemIbrahim 

 

For short bursts you would be able to log some data but you would not be able to do this continuously. Data would be the RMS of the last cycle updated every half cycle.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
DanL
Commander Commander
Commander

Re: Retrieving data from ION7650 power analyser in ms time frame

Yes, voltage and current can be configured to be recorded for short durations (based on event criteria) and then later retrieved using ION over the communications links.

Depending on your application requirements, you may choose to:

1. record instantaneous voltage and current in a Waveform Recorder
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=WaveformRecorderModule-045...

 

2. record one-cycle RMS every half-cycle in a Data Recorder (using a set of other helper modules to control trigger and enable logic)

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=DataRecorderModule-21B4C52...

Tags (1)