Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Regarding web interface of the HDPM6000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Regarding web interface of the HDPM6000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
573
Mehran_Mehrnia
Mehran_Mehrnia Champion
210
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-24 11:00 PM

0 Likes
3
241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-24 11:00 PM

Regarding web interface of the HDPM6000

Hello,

 

When connecting the HDPM6000 and a PC in a 1-to-1 setup and accessing the web interface via Chrome,

after logging in everything works normally for a while.

However, occasionally, when trying to change settings on tabs like Alarm and clicking the Save button,

an error message appears and the settings cannot be applied. In such cases, if we try to log back into the browser with the admin password, an error message like “Admin already logged in” appears and we cannot log in. Restarting the meter’s control power restores the system and we can log in again. Are there any possible causes you can think of?

 

Also, even though the browser setting is configured to automatically log out after 3600 seconds, there are cases where it logs out earlier than that. Are there any possible causes for this as well?

Regards,

Okada

Labels
  • Labels:
  • HDPM6000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-27 09:39 AM

0 Likes
0
201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-27 09:39 AM

Hi @T.Okada 

 

 

The behavior you are seeing may be related to the HDPM6000 login session management.

 

1. "Admin already logged in" message

For HDPM head units running system firmware v0.62 or later, the embedded web server uses HTTPS communication.

Only one Admin session can be active at a time. If an Admin user is already logged in from one browser and another login attempt is made from a different browser or PC, the message "Admin already logged in" can be displayed.

In this situation, it is not necessary to reboot the meter. Instead, enter the Admin password and click Logout. This will terminate the existing Admin session and allow a new login.

 

2. Unable to save configuration changes

The inability to save settings may be related to the same session management behavior.

For example:

  • User 1 logs in and opens a configuration page (such as Alarms or Channel Configuration).
  • User 2 subsequently logs in from another browser or another PC.
  • User 1 may still see the configuration page and appear to have access.
  • However, User 1's session is no longer active. When User 1 attempts to save changes, the save operation may fail because the original login session has been terminated.

This can create the impression that configuration changes cannot be applied, even though the root cause is the inactive session.

 

3. Network interruption while logged in

Another possible cause is a temporary network interruption.

If a user is logged in and the network connection between the PC and the HDPM6000 is lost and then re-established, the web page may still appear to be logged in. However, the original session may no longer be valid.

In this condition, attempts to save changes can result in an error even though the user interface still appears accessible. The recommended recovery method is:

  • Enter the Admin password.
  • Click Logout to clear the stale session.
  • Log in again.

A power cycle of the meter should not be required.

 

4. Logout occurring before the configured 3600-second timeout

The same scenarios described above could also explain why logout sometimes appears to occur before the configured 3600-second timeout.

For example:

  • Another Admin user logs in from a different browser or PC.
  • A network interruption causes the current session to become invalid.

In either case, the original user session may be terminated before the configured timeout period expires, which can appear as an unexpected or premature logout.

 

Therefore, please verify whether:

  • Multiple browsers, browser tabs, or PCs are accessing the HDPM6000 simultaneously.
  • Any temporary network interruptions are occurring between the PC and the HDPM6000.

If either condition exists, it could explain the observed behavior. In these situations, the recommended action is to enter the password, use the Logout function to clear the existing session, and then log in again rather than rebooting the device.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-27 09:39 AM

0 Likes
0
202
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-27 09:39 AM

Hi @T.Okada 

 

 

The behavior you are seeing may be related to the HDPM6000 login session management.

 

1. "Admin already logged in" message

For HDPM head units running system firmware v0.62 or later, the embedded web server uses HTTPS communication.

Only one Admin session can be active at a time. If an Admin user is already logged in from one browser and another login attempt is made from a different browser or PC, the message "Admin already logged in" can be displayed.

In this situation, it is not necessary to reboot the meter. Instead, enter the Admin password and click Logout. This will terminate the existing Admin session and allow a new login.

 

2. Unable to save configuration changes

The inability to save settings may be related to the same session management behavior.

For example:

  • User 1 logs in and opens a configuration page (such as Alarms or Channel Configuration).
  • User 2 subsequently logs in from another browser or another PC.
  • User 1 may still see the configuration page and appear to have access.
  • However, User 1's session is no longer active. When User 1 attempts to save changes, the save operation may fail because the original login session has been terminated.

This can create the impression that configuration changes cannot be applied, even though the root cause is the inactive session.

 

3. Network interruption while logged in

Another possible cause is a temporary network interruption.

If a user is logged in and the network connection between the PC and the HDPM6000 is lost and then re-established, the web page may still appear to be logged in. However, the original session may no longer be valid.

In this condition, attempts to save changes can result in an error even though the user interface still appears accessible. The recommended recovery method is:

  • Enter the Admin password.
  • Click Logout to clear the stale session.
  • Log in again.

A power cycle of the meter should not be required.

 

4. Logout occurring before the configured 3600-second timeout

The same scenarios described above could also explain why logout sometimes appears to occur before the configured 3600-second timeout.

For example:

  • Another Admin user logs in from a different browser or PC.
  • A network interruption causes the current session to become invalid.

In either case, the original user session may be terminated before the configured timeout period expires, which can appear as an unexpected or premature logout.

 

Therefore, please verify whether:

  • Multiple browsers, browser tabs, or PCs are accessing the HDPM6000 simultaneously.
  • Any temporary network interruptions are occurring between the PC and the HDPM6000.

If either condition exists, it could explain the observed behavior. In these situations, the recommended action is to enter the password, use the Logout function to clear the existing session, and then log in again rather than rebooting the device.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
T.Okada
T.Okada
Contributor

Posted: ‎2026-08-27 05:35 PM

0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-27 05:35 PM

Hello @Mehran_Mehrnia ,

 

Thank you for your response.

In all cases, the PC was connected one-to-one with the HDPM6000 head unit. Additionally, I verified that only one browser was open, with a single tab.

Given the one-to-one setup, I believe the network connection was stable.

In this case, I enabled the “phase V watchdog” while there was no voltage input.

Could that have caused the error?

Regards,

Okada

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2026-08-28 08:14 AM . Last Modified: ‎2026-08-28 08:24 AM

0 Likes
0
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2026-08-28 08:14 AM

Hi @T.Okada 

 

In my testing, where the PC was connected to the HDPM6000 over the network rather than in a direct one-to-one configuration, and with the Auto Logout Time set to the default value of 3600 seconds, the Phase V Watchdog, when enabled, caused periodic measurement recovery cycles when no voltage was present. However, it did not log out the user or invalidate the web session.

Mehran_Mehrnia_0-1787929763617.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore