Hi @T.Okada
To comply with power quality standards like IEC 61000-4-30 Class S, depending on selected 'Aggregation Method', the PM8000 processes harmonics using specific time windows that are updated every 3 seconds (which is default and represents a 150-cycle window at 50 Hz or a 180-cycle window at 60 Hz) or every 10 minutes.
You will find more information in ION Reference -> Harmonics Measurement Module
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @T.Okada
To comply with power quality standards like IEC 61000-4-30 Class S, depending on selected 'Aggregation Method', the PM8000 processes harmonics using specific time windows that are updated every 3 seconds (which is default and represents a 150-cycle window at 50 Hz or a 180-cycle window at 60 Hz) or every 10 minutes.
You will find more information in ION Reference -> Harmonics Measurement Module
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Mehran_Mehrnia,
Thank you for your prompt reply.
I understand the measurement cycle of the harmonics
and I checked it with the actual device, and it was just as you say.
Regards,
Okada